Sub panel grounding

dustinfox
11 years ago

Hi, I read the FAQ titled "What you need to know about installing a sub-panel" and I have one question. When running individual wires through conduit, why do I need a ground wire from the main building/panel if I am driving ground rods for grounding at the remote sub-panel? Seems like I could do without one or the other.

Thanks!

Comments (8)

  • Ron Natalie
    11 years ago

    Because it's required by the code. If you're within the same structure, all grounds need to be bonded together. If you're talking about a sub panel in a separate structure, the later codes for all systems (and the earlier ones when there is any other metallic connection between the building, e.g., phone, piping, cable) requires a ground as well as a grounded conductor.

  • terribletom
    11 years ago

    The ground rod(s) and the equipment ground from the main panel serve different purposes:

    1. The ground rod (earth ground) is capable of dispersing low-current/high-voltage surges -- typically lightening strikes in the case of a remote subpanel. Due to the high resistance of soil, however, it is almost useless when it comes to tripping a breaker in the event of an overcurrent situation (e.g., a ground fault in an appliance or other piece of equipment). A typical ground rod is capable of providing a return path to the center core of the power company's transformer for only about 5 amps or less.

    2. OTOH, the equipment ground from the main panel is bonded to the neutral at the system bonding point and provides a good low-resistance path to the transformer. That's the path that will cause a breaker to trip in the even of an overcurrent situation.

  • dustinfox
    Original Author
    11 years ago

    Thank you terribletom for answering my question!

  • dustinfox
    Original Author
    11 years ago

    One more question... At what level does voltage drop become a concern? i.e. if I start out with 120 volts at the main, how much of a loss is acceptable before it becomes a concern (loss of power, motors running hot, etc.)

    Thanks again!

  • brickeyee
    11 years ago

    3% is a typical max for conductor drop.

    Since it is normally computed at full rated current it is very rare for it to actually happen (adding some additional margin).

  • dustinfox
    Original Author
    11 years ago

    Thanks brickeye... I'm considering running 6/3 copper to a barn 130 feet away (to the sub panel) which puts the voltage drop right around 3% at 60 amps. Sounds like I'm ok then!

  • brickeyee
    11 years ago

    Make sure you account for both directions (current out to the panel, and then the return current).

    Some SW is 'smart' enough to double the distances using the same gauge, others need each side computed separately (especially if the wires are not the same size).

  • dustinfox
    Original Author
    11 years ago

    I used a calculator I found on the internet here

    http://www.csgnetwork.com/voltagedropcalc.html

    I will calculate manually to double check. Thanks again!