| I have a portable Generac GP7000 that is gasoline powered. I would like to have it converted to a natural gas/propane using a kit from US Carburetion as I have natural gas.
The kit would cost me $267.00. The problem is that my "Gen In" plug, electric meter, transfer switch and breaker box are all on the NORTH end of the house on same wall. The natural gas meter is on the SOUTH end of the house 60' away from the opposite side of the electric meter/genset inlets. The natural gas pipe from the meter goes up the south side of the house and into the attic heading straight north. It T's off & branches down a wall to feed a gas central heat unit, which I would NOT use in a power outage. The pipe continues northward in attic and branches down to my gas range, which I would NOT use in a power outage. The gas pipe continues north in attic and branches down to a 1/2" yellow hose add-on feeding an outlet to a gas grill on the west side of the house. Finally the gas pipe continues northward into the laundry room which houses my transfer switch & breaker panel and goes down a wall to my gas water heater in the same room--which I would use in a power outage. The gas pipe in the attic that L's down to the water heater is only 10 feet from the NORTH wall by my GEN IN plug. Most natural gas generators I see are hooked right up near the gas meter and conversion kit manufacturer says to use a 3/4" or 1" hose on ground to run to generator. This hose would be about 100" by the time I snaked it around corners of house etc...this would be very expensive too. My gas meter does have one of those little removable plugs on my side of the meter as it elbows from meter and enters house--this is where people say to hook up a generator too with a cutoff there. I am trying to avoid a costly hose. Plus the gas meter is right by my bedroom window--don't really want a genset running right there, plus my neighbor's room is just a few feet away. The NORTH end of the house has nobody next door to me except a busy highway, plus the north end of the house is the laundry room and noise in house from genset is no problem. It would be much more economical for a plumber to tie into the gas pipe in the attic where it elbows down on the end of the gas pipe run and goes to water heater and exit this pipe out of the north end of the house and down to genset--less than 16' iron piping total. The 1/2" gas grill connector coming out of exterior west wall is only 5' from my genset plug, but again, this line is only 1/2"...don't know if it would work or not by just connecting a 5 foot run of 1" hose to it & going to genset on exterior of house. My question is do any of you have a portable natural gas generator...if so how big of a gas pipe do you need to power a converted gasoline to natural gas genset? This may be a plumbing question. My apologies if I posted in wrong forum. |
Follow-Up Postings:
|
- Posted by ronnatalie (My Page) on Mon, Jul 4, 11 at 21:04
| My propane powered 80KVA generator is only feet from the propane tank and has a rather hefty size pipe running to it. I suspect you'd be best served by following their instructions even if it means running a new line all the way back to the meter/regulator. |
|
| Assuming 1000BTU/cu.ft. gas, your set will consume about 140-150 cu.ft. per hour at full load. Give that information to a competent gas installer and the pipe size needed can be calculated. |
|
- Posted by ronnatalie (My Page) on Mon, Jul 4, 11 at 22:30
| The manufacturer already mandated 3/4". That's pretty much what you need to go with. Unlike water, there's not much friction loss with natural gas. |
|
- Posted by jeanie_beth (My Page) on Mon, Jul 4, 11 at 23:20
| Thanks guys for the replies. I guess what I was really meant to ask, is if that is a 3/4" line that is in the attic, is it OK to hook to the end of the 3/4" pipe (where it goes down to water heater) and go to the genset even though there are T's off to the furnace and stove BEFORE the gas goes to the genset or does the pipe just need to be a dedicated 3/4" line coming right out of meter and not have any branching to other devices? In other words, is gas flow more powerful coming right off the meter and straight to the 60' or so underground to the genset or is it same pressure as coming out of meter, up wall, into attic, to other gas devices and then to genset via attic? I'm sure that the main gas line in attic is indeed 3/4" with 1/2" lines branching down to stove, furnace, gas grill.
|
|
- Posted by bus_driver (My Page) on Tue, Jul 5, 11 at 7:30
| I wonder why the gas appliances and furnace would not be used in a power outage? If Winter, how to heat the house? The purpose of the generator is to supply the relatively small power requirements of the furnace so that it is usable. |
|
- Posted by jeanie_beth (My Page) on Tue, Jul 5, 11 at 10:04
| Our winters are mild--we hardly even turn on the gas central heat in the winter because it dries my skin out and causes severe nose bleeds on myself. As for cooking with the gas range, if the power outage were in the winter, I would only briefly cook with it. If the power outage were in the summer, I wouldn't cook on it at all due to adding more heat to the home. I never use the oven on it from May-October even with power on..if I use the stove at all in summer, it is briefly stove top--we grill outside just about everyday on the patio. If the winter is cold and power is out for a long time, we have a 12' x 22' insulated metal building with a 8000 BTU window unit and natural gas heater and a trundle bed in it and PC & TV--all of which has its own separate transfer switch and genset if worse comes to worse and I need heat in winter. |
|
- Posted by stinkytiger (My Page) on Thu, Jul 7, 11 at 12:44
| Hi, I have a generator which is hooked up to a propane tank, 20,000 Watts Cummins Onan RS 20,000. This has a 4 cylinder Ranger engine made by Ford. The gas line is 3/4 inch and runs from the propane tank. The gas line by code is limited to 100 feet (New York state). And you cannot have an underground join in the gas line. The gas line does not have to be very big because the propane is under presure and when under pressue it is actually a liquid. Right by your generator the gas line will connect to a Regulator. This regulator "converts" or more accurately will allow the propane to expand. The propane then becomes a gas and be at a lower pressue. This gas is then passed into the "propane carbaretor" which you will mount on your genset. So a relatively thin line can feed quite alot of propane because of the liquid to gas transformation. Things to watch out for a Carbon Monoxide poisoning. I would not site the genset near any windwows near a house. Also having a high pressue gas line snaking all over your house could be a fire risk and may not be allowable by code. Note if you bury the propane line, you only have 100 feet to play with and you have to bury it deep. This means expensive. Think a back hoe or some mechanical digger. If you are going to all the troule with the gas line etc., maybe it would be worth it to consider a new genset as well. warmest regards, Mike. |
|
| "The manufacturer already mandated 3/4". That's pretty much what you need to go with. Unlike water, there's not much friction loss with natural gas." Inlet size does NOT determine needed pipe size to deliver gas. The tables are in the back of the plumbing code usually. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.