220v lines to irrigation pump

Posted by rob46 (My Page) on
Wed, Jul 1, 09 at 16:30

I'm installing a 220v pump that requires 10ga. wires for the run. Is 10ga. also required for the neutral/ground or would 14ga. be sufficient, as it is already there.
Thanks, Rob


Follow-Up Postings:

 o
RE: 220v lines to irrigation pump

For a circuit wired with #10 the ground must also be #10.


 o
Also,....

I forgot to mention. A 240v pump will not have or require a neutral.


 o
RE: 220v lines to irrigation pump

Thanks petey, and I had started to wonder about the neutral situation for a follow up but you covered it.