Is 1.5 inches enough.

bugbite
10 years ago

The initial question was about how much protection for a wire is code.

Also about wiring in Crown Molding. An excellent discussion about that exact topic is located in the link a couple of posts below. So if you are interested in a discussion about wiring in crown, check that out.

The answer to my question is in the link below about code 300.4.

Thanks for those who clarified the word "conduit", certainly helpful.

Thanks ronnadaile for directing me to code 300.4

This post was edited by bugbite on Thu, Jul 11, 13 at 12:10

Comments (13)

  • Ron Natalie
    10 years ago

    This isn't conduit. Calling it such is confusing.
    While it sounds like if you are planning to run NM cable in such an enclosed area it would be legal, but the conditions is WHY?

  • btharmy
    10 years ago

    1. staple the nm cable in the corner of the ceiling to wall
    2. make your drops down the wall where you need to
    3. cover the cable with crown

    I don't see any reason to over engineer anything more than that.

  • bugbite
    Original Author
    10 years ago

    Ronnatalie, Thanks for the comment.

    Just found a discussion about my issue. Ten years old, but interesting.
    See discussion in link below.

    Here is a link that might be useful: A discussion about this

    This post was edited by bugbite on Thu, Jul 11, 13 at 11:03

  • bugbite
    Original Author
    10 years ago

    Btharmy, Thanks!
    I am an Engineer. But I have never been accused of over engineering. Maybe it's retirement. :-)

    This post was edited by bugbite on Wed, Jul 10, 13 at 22:22

  • petey_racer
    10 years ago

    WHY are you over-thikning this. You say an electrician is doing the work? Let him do it.

  • bugbite
    Original Author
    10 years ago

    Petey.

    He will do the wiring.

    I will do ALL the sheetrock work.

    I got my answer, which is "yes". So I withdrawn the question.

    Thanks all.

    This post was edited by bugbite on Wed, Jul 10, 13 at 22:28

  • petey_racer
    10 years ago

    Going in an editing all your posts hours after just because you got a reply you liked is extremely poor forum etiquette.
    WHY would you bother doing that??

  • petey_racer
    10 years ago

    IMO this thread should not only be locked it should be removed completely.

  • Ron Natalie
    10 years ago

    In electrical work, conduit has a defined meaning. Your use is not IT.

    What you have here is a non-listed non-metalic wire way. It has no status as far as an electrical raceway. It's just a piece of the building. You can use other listed wiring methods within it (i.e., NM cable). Given the size of the wood, you'd not have to worry about physical damage (300.4 tells you what you have to do to enclose wiring in wood structural members).

    However, what you are proposing is a lot of work for little benefit. You can pull NM behind the crown or just put it in the wall (I'm not sure why you don't want people drilling through your top plate). You can't use conductors not approved to be run by themselves. This wood box is not any sort of legal conduit or raceway.

  • bugbite
    Original Author
    10 years ago

    Petey, You are right; remove it. I certainly support that.

    Wish I just asked which code covers : "Protection Against Physical Damage." Didn't know what to ask when I wrote the question.

    Thanks ronnatalie . This info is very helpful:
    " Given the size of the wood, you'd not have to worry about physical damage (300.4 tells you what you have to do to enclose wiring in wood structural members)."

    "You can't use conductors not approved to be run by themselves. This wood box is not any sort of legal conduit or raceway."


    Regarding: "I'm not sure why you don't want people drilling through your top plate".
    I could care less if they drill through the top plate. They will do that all over in the 14 other rooms in this big house. The 2 rooms I am discussing alternatives for here (one bath and one bedroom) are VERY difficult to access from above. I am having to cut large holes into a textured ceiling just to get the wire into each room.

    The challenge is how to get the wire all the way around these two rooms without having to do major sheetrock repair all the way around these rooms.

    Sure would be sweet if they could come in through the top plates like the rest of the rooms.

    Here is a link that might be useful: 300.4

    This post was edited by bugbite on Thu, Jul 11, 13 at 9:54

  • Ron Natalie
    10 years ago

    The big issue is you either have some incredibly large rooms or your oversizing crown molding if you intend to use a 3 1/2 channel behind it.

  • bugbite
    Original Author
    10 years ago

    See link for an example of a crown that could support this channel see " Holmdel Traditional Smooth Crown Moulding" Right side. Of course it would demand a transitional piece at the bottom for a total height of about 5". I will not use this but will build something with a similar profile to adapt to the 3 1/2" high core.

    My favorite woodworking thing is building crown. So no worries.

    Thanks for all your help.

    I think this question has been exhausted so I will not revisit this post. Thanks Again.

    Here is a link that might be useful: Holmdel Traditional Smooth Crown Moulding

  • Ron Natalie
    10 years ago

    The issue is that if he is trying to cover up a 3.5" box behind the crown, it's going to take a 10" measured on the backside) piece of crown to do it.

    That's going to dwarf most people's room scale.