Seems to make no sense using 14/3 for a split plug on a kitchen counter. it means that the common can carry up to 30 amps. how is this legal? code book tells me that's what I need to use


Follow-Up Postings:

 o
RE: Counter Receptical

The neutral in a multi-wire branch circuit only carries the current imbalance, NOT the combined current of the two hots.

I assume you are in Canada?


 o
RE: Counter Receptical

Happy Canada Day BTW!!


 o
RE: Counter Receptical

When you add together things like the sine waves of voltage you have to know the phase difference between the waves.

The two legs are 180 degrees out of phase.

If you put equal loads on each 120 V leg, the resulting current in the neutral wire is zero.

The advantage of the 'Edison system' like this is that we can have 120 V to ground for safety, but between the legs get 240 V for larger loads.


 o
RE: Counter Receptical

Yes it was Edison that did the three wire service, but it had naught to do with sine waves nor 240V loads. It was DC and all the loads were 100V (the nominal voltage being 110 to deal with resistive loss). The reason for a +110/0/-110 distribution system was to save on wire. The entire system was a giant MWBS.


 o
RE: Counter Receptical

"...but it had naught to do with sine waves nor 240V loads"

We use the system since it allows for larger loads at 240 V while maintaining the safety of having a maximum of 120 V to ground.

It is true that it also works for DC systems, but only if the DC is configured in the same way.

Edison's chief problem with using DC was the inability to take advantage of higher distribution voltages to reduce line loss.

The lowest distribution voltage in the US is 7.2 kV.
It runs up to almost 500 kV for a very few long distance lines, and up to 1 MV for some special DC lines (we now can convert the DC back to AC using SCRs, large stacks of SCRs).


 o
RE: Counter Receptical

I'm a bit confused. if I plug in a toaster and a kettle in the split receptical, the common doesn't carry both loads? Am I missing something? and yes I'm in Canada. thanks for the fast reply's. I'm glad I found this sight. thanks again


 o
RE: Counter Receptical

basically the toaster will return through the kettle. Any difference in amperage between the two will be carried on the neutral wire. Just like the whole house, 3 wires come in (all the same size, sometimes even smaller for the neutral). One leg carrying 80 amps and the other carrying 95 amps (just an example), the neutral only sees 15 amps. In that scenario the neutral is allowed to be smaller because it is unlikely that 200 amps would ever be used on one leg with 0 amps being used on the other leg (200 amp service in example). In your 15 amp scenario, the most your neutral will see is 15 amps. If some moron were to move breakers around so that the black and red are on the same phase, the neutral code potentially see 30 amps. That would not happen since you have to use a double pole breaker anyway. Don't forget to check GFCI requirements, if GFCI protection is required, you will have to use a double pole GFCI breaker.


 o
RE: Counter Receptical

Thank You Spencer. The panel I'm using is a stablock and it is possible to put a double breaker in this make of panel on the same leg. I found it out when I hooked up an oven/range and the oven wouldn't heat (but the clock worked). I'll have to make sure that I put the breaker in the right position in the panel. Sounds like that type of panel needs a safety upgrade. Thanks so much


 o
RE: Counter Receptical

> The panel I'm using is a stablock ...

Change it. I wouldn't knowingly sleep in a house with one of those panels.

Here is a link that might be useful: FPE Stab-lok Panels


 o
RE: Counter Receptical

For some reason, the FPE panels in Canada are not the same problem as the are in the US. I believe they are still newly installed to this day.
Maybe one of our regulars from Ca can shed some light.


 o
RE: Counter Receptical

Oops, sorry, I didn't see that he was in Canada.

I've read too that the Canadian FPE panels were OK. No idea what the difference was / is.


 o
RE: Counter Receptical

"I've read too that the Canadian FPE panels were OK. No idea what the difference was / is. "

The panelsare not so much a problem as the breakers,


 o
RE: Counter Receptical

FPE in Canada is Fereral Pioneer as oppposed Federal Pacific in the USA.
FPE is still a very popular panel in Canada. They were made by a different company than the ones in the USA. Schneider Electric makes them now.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here