meter problem?

Posted by rati0nal (My Page) on
Mon, Jul 26, 10 at 14:08

my electric stove which needs 240V does not work. all the appliances work except electric stove. circuit breaker only reads 120V. it seems we have only L to N reading: 120V no L to L reading (240V). multimeter shows 240V before the electric meter outside and 120V after the meter. is this a meter problem? a single phase meter installed instead of multi phase meter?


Follow-Up Postings:

 o
RE: meter problem?

You have single phase 120/240 V service.

It is possible you have a dropped 120 V leg.

Any 120 V loads on that leg should not be working either.

You can turn the stoves breaker off and then back on to see if it has one pole not closed.

The next thing would be to check either the stoves receptacle, or open the panel and check directly on the stoves two pole breaker for both 120 V from each leg to neutral and 240 V between the legs.

DO NOT OPEN THE PANEL if you are not VERY sure of what you are doing.

You will be measuring voltages in a HOT panel and need to be careful to not touch ANYTHING else in the panel.


 o
RE: meter problem?

If he has measured before the meter, then he's had THAT open. The panel isn't worse.

My guess: one side of the service is open (corroded connection or somesuch) and one of the 240V loads in the house is providing a connection (albeit a resistive one) allowing the good leg to feed the open one.

My prediction is, if the original poster turns off all of the double-pole breakers, half of the 120V circuits will stop working.

In any case, the solution is to find where the connection is broken and fix it. If there is 240V at the line side of the meter, then the failure is at the terminals on the load side of the meter base, the terminals on the main breaker, the cable in between, or the main breaker itself. Failure inside the meter is theoretically possible but I've never seen it.


 o
RE: meter problem?

"If he has measured before the meter, then he's had THAT open."

Or he measured at a weather-head splice.

"The panel isn't worse."

Sort of.

There are a lot more things in the panel to touch accidentally than the few contacts in a meter base or weather-head connection.

Agree with shutting off all the 240 loads and seeing it one leg is back feeding the other.
The voltage might be a little low, but if the 240 V load is large enough it could still be within the normal 10% variation allowed.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here