Lutron receptacle?s

Posted by footwedge (My Page) on
Sat, Jul 23, 11 at 13:50

I was installing the new lutron receptacles for the small appliance circuit. The original installation consisted of a 20 amp gfi followed by 3-15 amp receptacles protected by a 20 amp breaker. I did not notice the existing gfi receptacle was 20 amps until now. The existing cable is 12-2.

I ordered a lutron 15 amp gftr receptacle and 3-15 amp receptacles to replace the existing. I found this discrepancy while I was trying to connect the ground wire to the 15 amp gftr. I tried numerous times and the ground screw will not back out enough to allow the #12 to get behind. I tried a scrap piece of #14 and it fit.

My questions are:

1. Should I have ordered all 20 amp receptacles for the small appliance circuit?
2. or will it be ok to install just like the original- 20 amp gfi followed by 3 15 amp receptacles?
3. will a 20 amp gftr allow more space to connect the #12 ground? I'm thinking it will be the same as a 15 amp gftr but not sure.


Follow-Up Postings:

 o
Did some research and

and found that it is acceptable to put a 15 amp receptacle on a 20 amp non dedicated circuit. I also checked several existing duplex receptacles on other 20 amp circuits and they are all 15 amps.

So now my question is, should I change the gftr to a 20 amp leaving the others at 15 amps or continue to try to connect the ground (#12) to the 15 amp gftr?

Lutron tech support recommended 20 amp duplex receptacles if protected by a 20 amp breaker. They also said the ground screw on the 20 amp gftr will back out more allowing connection of the #12. They must very tight specs on the construction of the 15 and 20 amp gftrs.


 o
RE: Lutron receptacle?s

"Lutron tech support recommended 20 amp duplex receptacles if protected by a 20 amp breaker. "

Simply wrong.

You will probably not have any 5-20P plugs.
Use 5-15R or 5-20R receptacles.
The NEC allows use of 15 amp devices on 20 amp circuits as long as there is more than 1 receptacle (and a duplex is of course two).

Here is a link that might be useful: NEMA Plug & Recep configurations


 o
RE: Lutron receptacle?s

ThanksBrickeyee,

What are your thoughts on the 20 amp ground screw backing out more than the 15 amp one so it can accept the #12?

I guess this could be possible.


 o
Finally got the ......

#12 on the ground. Finished wiring the remaining receptacles with all passing the tester. Making Progress.


 o
RE: Lutron receptacle?s

"What are your thoughts on the 20 amp ground screw backing out more than the 15 amp one so it can accept the #12? "

Sounds like something an outsourced customer service department would say. The 15A GFCI is designed to be used on a 20a circuit. It is more common for it to be used there then on a 15A circuit now since the locations that require GFCI mostly require 20a circuits - kitchens and baths. It most certainly will work with 12 gauge wire.

If you can't get the screw to back out further, that is more to do with forearm strength than design. Unless the receptacle is damaged, the wire will fit.


 o
RE: Lutron receptacle?s

The Lutron GFCIs have a plate under the ground screw you just slip the ground wire under then tighten down... no need to wrap around the screw.


 o
RE: Lutron receptacle?s

"What are your thoughts on the 20 amp ground screw backing out more than the 15 amp one so it can accept the #12? "

BS. 15 amp duplex receptacles are rated for use on 20 amp circuits with #12 wire.


 o
RE: Lutron receptacle?s

BS. 15 amp duplex receptacles are rated for use on 20 amp circuits with #12 wire.

That's what I thought.


 o
RE: Lutron receptacle?s

You do need to be aware that working #12 is slightly more difficult than #14.

A receptacle with 5 #12 conductors (2 hots, 2 neutral, 1 ground) takes a decent amount of force to fold the wiring back into the box.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here