Standby Generator wiring to Transfer Switch

Posted by caseyc0815 (My Page) on
Sat, Jul 10, 10 at 13:33

My 20kw Generator is located approx 30ft from the Automatic Transfer Switch location. The genset has a double 100amp (each) breaker near the control panel. Internally, the power wires are connected to one side of each breaker. The wires going to the transfer switch get connected to the other side of each breaker. The internal wires look like they are #6AWG possibly #4 (can't make out any size printing on the wire) but its about the size of sparkplug wire and stranded. What size wires would be required to connect the other side of the breakers to my transfer switch 30 feet away?


Follow-Up Postings:

 o
RE: Standby Generator wiring to Transfer Switch

Your inspector might say otherwise, but here it would be fine on #4 copper or #2 aluminum.


 o
RE: Standby Generator wiring to Transfer Switch

"The internal wires look like they are #6AWG possibly #4 (can't make out any size printing on the wire)..."

The wires inside the unit do not follow the NEC.

They can be different insulation that the NEC does not even allow in permanent wiring by trhe NEC .

Equipment wiring is covered (at least in part) by NEMA.


 o
RE: Standby Generator wiring to Transfer Switch

I would use 2 cu or 1/0 al.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here