Thu, Jul 7, 11 at 12:53
| I'm helping my daughter with a new house. She will have an un-finished basement.. Just used for storage. Does it have to be wired or no as far as wall receptacles? |
Follow-Up Postings:
|
- Posted by ronnatalie (My Page) on Thu, Jul 7, 11 at 15:25
| An unfinished basement must have at least ONE receptacle in it and it must be GFCI protected. If the furnace/heatpump/airconditioner is located there, there must be a receptacle within 25 feet of it (it can be the ONE mentioned above). |
|
| Bringing the circuit down the inside of the block wall, will the wire 12/2 need to be in conduit? If so, is PVC acceptable or does it need to be thinwall? |
|
- Posted by ronnatalie (My Page) on Fri, Jul 8, 11 at 20:40
| Conduit is not mandatory. As long as you're not in an area subject to physical damage you can surface mount the NM. If you do need protection from physical damage you can use Sched 80 PVC (as well as the metal conduits). |
|
| I agree with Ronnatalie, except in certain locations (like Chicago) where the local rules require conduit. Check your local regulations. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.