| When I opened the electrical panel in a house we recently purchased, I was surprised to find the following. For all of the circuits, the neutral wires and their respective ground wires are attached together to the ground bar. And the neutral bar is empty.
The house was built in 1963. The cable is cloth covered Romex with ground. In 2005, the previous owner increased the service to 400 Amps and installed two Siemens panels (200 Amps each) and new Siemens breaker switches. One of the panels feeds a 100 Amp subpanel located in the garage. Outside of the house, a new panel and two master breaker switches (one breaker for each of the two 200 Amp panels) were also installed with a new meter. Ground wires run from the outside master breaker panel to a rod directly below it in the ground and a second wire runs inside and connects to the water supply line. The water supply line transitions from copper to PVC inside the basement, near the point of entry to the house - PVC runs to the street. Questions:
TIA |
Follow-Up Postings:
|
- Posted by ronnatalie (My Page) on Thu, Jul 8, 10 at 13:46
| At the main disconnect (typically the main panel), ground and neutral are bonded together and using the same bar for neutrals and grounds is permissible. In other places, the grounds and neutrals must be kept separate all the way back to the main disconnect. You need a neutral bar isolated from the grounds. What you describe would be fine if this were the main panel. However, it seems like the main disconnect is not either of the Siemens panels are subpanels. You are right, the neutrals should be on their own bar electrically isolated in that panel from the ground. As for the pipe, if the interior piping is copper (regardless of the external connections), it needs to be bonded. This isn't providing an additional ground (like connecting to the incoming metallic pipe would), but providing safety in case some live wire should come in contact with the interior piping that would engergize all your faucets ,etc... |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.