30 or 40 amp circuit for this double wall oven?

Posted by seang86s (My Page) on
Thu, Jul 10, 08 at 0:44

Can I install a 10 gauge, 30 amp circuit for this Electrolux double wall oven? The spec sheet says:

Amps @ 240 / 208 Volts = 33.3 / 28.9 Amps

I was planning on an 8 gauge, 40 amp circuit but I'm having trouble sourcing the cable (I already got the breaker from my local home center).

Here's the original spec sheet: http://www.electroluxicon.com/files/international_english/0-999/E30EW85ESS_specs.pdf


Follow-Up Postings:

 o
RE: 30 or 40 amp circuit for this double wall oven?

No, the spec is 33 amps so you must use a 40A breaker with at least #8cu.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here