Two outlets in 2 gang being fed with different phases.

Posted by orourke (My Page) on
Sat, Jul 2, 11 at 0:38

In my garage, a 2 phase Rommex wire (Black,Red,White,Ground) comes, presumably from the attic, and feeds two separate outlets in a two gang outlet. So the white wire is shared, while the black phase feeds one outlet and the red phase feeds the other outlet. I’ve never seen this anywhere else in my house so I’m wondering is this ok? That is, to feed two adjacent outlets with different phases sharing the white neutral?

P.S. I know the black and red are different phases because there is 220 voltage between them.

P.S2 I have a question about CGFIs related to the above, but I’d thought I’d first ask the question above.


Follow-Up Postings:

 o
RE: Two outlets in 2 gang being fed with different phases.

What you have is a multi-wire branch circuit (MWBC). Properly installed, they are perfectly acceptable and legal. The key point is that the two hots must be on opposite legs in the panel. Because of the way A/C works, two legs are out of phase by 180 degrees so the neutral carries the difference in current between the two legs. It's biggest advantage is cost savings because you save one [neutral] wire for every two circuits.

Frankly, I'm not overly fond of them in residential setting because people don't understand what's going on and there's the potential to get zapped. It's critical to shut off both breakers when working on a MWBC. The rules say that the breakers should be tied so that both are turned off at the same time but that doesn't always happen.

Let's say that you have a room where a wall receptacle and overhead light are opposite legs of that MWBC and you decide to replace the receptacle. Unaware it's a MWBC and because the idiot who installed it didn't tie the breakers, you turn off the breaker for the receptacle and test it. It's dead and you start pulling things apart. Because you want to see better you flip on that overhead light. The receptacle will still test dead but as you're handling the neutral you hand brushes up against the grounded metal box. You get zapped. It's not likely to kill you but it's going to hurt. Change the scenario slightly where there's a table lamp plugged into the wall receptacle and you're up on a ladder working on the ceiling fixture. Get zapped slightly, naturally jerk back, loose your balance, and fall off the ladder.

So make sure those breakers are tied.


 o
RE: Two outlets in 2 gang being fed with different phases.

"The receptacle will still test dead but as you're handling the neutral you hand brushes up against the grounded metal box. You get zapped."

While there are risks to MWBC circuits, this on e is sort of a fantasy.
You are not likely to feel anything nut the most minor of shocks, the path through you and ground is not going to be a lower impedance than an intact neutral.

The bigger requirement is that neutral in MWBS circuits be pigtailed so that disconnecting a devices does not interrupt the neutral to other loads.


 o
RE: Two outlets in 2 gang being fed with different phases.

Thanks for the advice and definition of the terminology. So I have a question about CGFIs in this situation (which is what precipitated my first question in the first place), but since it is a different enough topic I have posted it separately.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here