Sizing of sub panels in multi-family dwelling and main service

Posted by spencer_electrician (My Page) on
Thu, Jul 26, 07 at 0:03

I'm still in school to become a master electrician and I work with another master electrician. A recent job possibility has both of us a little confused. It is just 2 not as common situations combined together. A house needs to be wired as four units. Two upstairs and 2 downstairs. The general wants everything to be electric, no gas at all. Each unit needing a 12kva furnace, 10kva oven, 5kva dryer, and a hot water heater, 800 sqft. general lighting, laundry circuit, and 2 small appliance. A while back when I figured up a load calc it was right around 130 amps. Now of course all of these can be deducted since there are four units but what about the sizing of the sub-panels and meters? Is it the units need a 150 amp service while the whole building needs a 400 amp service? The boss keeps saying no, the units only need 100 amps because of deductions but I see it as the unit must have its calculated load available to the sub-panel. Where the main service, deductions may take place.

If 150 amps is the answer. Does such a peice exist? A meter assembly with 5 meters (One meter for general hallways) and 150 amp breakers with a 400 amp main?

Thanks for suggestions, it helps me learn planning these things whether they're for one of his jobs or just practice. I just can't seem to find this type of situation in the books.


Follow-Up Postings:

 o
RE: Sizing of sub panels in multi-family dwelling and main servic

The feeders and panels in the individual units need to be sized for the connected load. You do NOT size the service then divide by the number of units, less house load, to determine the feeder and panel size in the units.

A good review of the examples in Annex D should show you how this is done. When figuring the service size you are allowed to use 17KW for 4 ranges (not over 12KW each). This does NOT translate to only allowing 4.25 KW in each unit for a range, nor does it allow that since the 8KW has been used to calculate the unit feeder size that you can now use the 220.55 table column A and B to figure the service size if the range is over 8 3/4 KW.

As to the meter cans, main breakers, and service disconnect/OCPD, virtually any combination can be ordered. With rare exceptions you won't walk in to a distributer and buy exactly what you want off the shelf. Get a few service equipment catalogs and browse a bit.

Be sure your furnace includes the blower as this is often separate with electric heat, and water heaters come in a variety of sizes.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here