Q about derating

Posted by terribletom (My Page) on
Mon, Jun 28, 10 at 22:04

Hi folks! Just a quickie question here...

In planning a semi-busy conduit run, I'll have a couple of pairs of switched "travelers" (i.e., alternative hot paths running between three-way switches) in the same raceway. For the purposes of derating, does a pair of travelers count as one conductor or two?

From the standpoint of heat management, it strikes me that a pair should count as one, since only one can be an active conductor at any point in time. [OTOH, code doesn't always accommodate my intuitions and divinations. :-) ]

(Note: The question is not about conduit physical fill volume...just how to count conductors for derating calcs.)

Thanks much!


Follow-Up Postings:

 o
RE: Q about derating

The travelers should each be counted as a current carrying conductor, but remember, if this is a 15 or 20A circuit, derating will not affect wire size/circuit breaker choice until you exceed 9 current carrying conductors.


 o
RE: Q about derating

Thank you, Norm. Groan, that's pretty much what I suspected the answer to be.

In this case, it's a mix of 15- and 20-amp circuits and the plan is right on the bubble. That is, if two travellers count as one, then I have 8 total. Otherwise, I have 10.

Common sense suggests that it's a stupid reason to pull #10s instead of 12s and 12s instead of 14s when two of the conductors are guaranteed to be dead at any given time.

But, oh well, code is code whether it always makes sense in context or not.


 o
RE: Q about derating

I would count them as 1 same as when using a multiwire branch circuit the neutral doesn't count.
Don't confuse derating with conduit fill. Those are two different calculations.


 o
RE: Q about derating

For fill, two conductors.

For derating, a single conductor since they cannot both be active at the same time.

This is exactly analogous to a multi-wire branch circuit.

3-wires for fill, two for derating.

Remember you get to start with the actual conductor ampacity for derating (not the footnote limit of 15 A on #14 and 20 A on #12).


 o
RE: Q about derating

joed wrote: "I would count them as 1 same as when using a multiwire branch circuit the neutral doesn't count."

Now there's an answer I like better. :-) Thanks.

and brick':

"For fill, two conductors.

For derating, a single conductor since they cannot both be active at the same time.

This is exactly analogous to a multi-wire branch circuit.

3-wires for fill, two for derating."

Makes sense to me. Thanks.

Remember you get to start with the actual conductor ampacity for derating (not the footnote limit of 15 A on #14 and 20 A on #12).

Yup, capisce. Of course now that I'll only have eight, I'm home free anyway.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Instructions

  • You must be a registered member and logged in to post messages on our forums.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • It is illegal to post copyrighted material without the owner's consent.
  • HTML codes are allowed in the message field only.
  • No advertising is allowed in any of the forums.
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.



 
Click here to learn more about in-text links on this page.