Central AC wire sizing

peterbu
14 years ago

I am installing a 2.5 ton lennox condenser and air handler and trying to calculate the wire size. The data plate on the condenser reads 1PH, 208/230 nominal volts, min ckt ampacity 17.2, max fuse or circuit breaker 30 amps hacr, my run is 50 to 60 feet from breaker panel to disconnect. For the Air Handler the plate reads 208/230 nominal volts, min ckt ampacity 5, max fuse or circuit breaker 15 amps hacr, my run is 25 to 35 feet from breaker panel to disconnect. Most AC disconnects say 60 amps, that must be the max? Thank you very much.

Comments (13)

  • petey_racer
    14 years ago

    10/2 for the condenser.

    14/2 or 12/2 for the air handler.

    Yes, the 60a figure is the max rated amps. You an use it for anything up to 60 amps.

  • joefixit2
    14 years ago

    Why couldn't he use 12 for the condenser?

  • wayne440
    14 years ago

    A 30a breaker will be used with the condenser, so #10 wire is appropriate.

  • wayne440
    14 years ago

    You must enjoy resetting circuit breakers.

  • normel
    14 years ago

    Wiring to the compressor could be 12/2 or 10/2. The requirement that 10/2 be used with a 30A breaker does not apply for a compressor/motor.

  • joefixit2
    14 years ago

    "You must enjoy resetting circuit breakers."

    How would smaller wire make the circuit breaker trip??

  • brickeyee
    14 years ago

    "A 30a breaker will be used with the condenser, so #10 wire is appropriate."

    This is a hermetic compressor load plus a motor load for the condenser fan.

    Just like electric motors there is a separate code section covering the branch circuit requirements.
    The motors contain thermal overload protection preventing them from drawing excessive current.
    The wires are sized at 125% OF full load running current, and the breaker is chosen to allow for starting without tripping.

    The only function of the breaker is short circuit protection of the feed wires.

    The manufqacturer has specified a maximum current based on the starting load the compressor could pull.
    It is not used to size the conductors.

    Higher limits than a general purpose branch circuit are allowed and can be many time the full load running current.

    The wire size and breaker are no longer sized to match each other like general purpose branch circuits.

    The run is short enough that excessive drop is unlikely, even at the possible 30 amp starting current.

  • jpdime_yahoo_com
    12 years ago

    Good answer Brickeyee.

    Take the minimum ampacity in this case is 17.2 amps and multiply this by 1.25 which is 21.5 amps. Number 10 Awg is what is called for.

    And the manufacturer calls for a 30 amp breaker. And because this is a dedicated motor circuit meaning no other electrical devices are on the circuit we have to size accordingly.

  • bus_driver
    12 years ago

    Oversizing the conductors above the minimum to the outdoor unit of an AC or heat pump has some potential advantages. Voltage drop at the unit while starting is less than it is with smaller conductors. And running voltage drop is slightly reduced as well. It saves a little on the power bill.

  • petey_racer
    12 years ago

    Paul, WHY are you multiplying the MCA @ 1.25??

    The MCA is the MCA. 17.2A is 17.2A MINIMUM CIRCUIT AMPACITY.

    12/2 on a 30A breaker would be typical. 10/2 is fine, but for such a short distance I see NO need to oversize to #10.

  • petey_racer
    12 years ago

    My point is the 125% is ALREADY taken into account.

  • jmorrow
    12 years ago

    if you are putting electric heat strips in the air handler (highly likely unless you live in Hawaii), the strip kit will come with new ampacities that nullify what's originally posted on the unit. so if you are, check those specs so you don't end up having to do it twice. 12 is adequate for the heat pump.