Sat, Jun 16, 12 at 20:52
| What does the code say about the insulation requirements for the hot, neutral and ground in a metal conduit? I would like to know if I can strip the outer jacket of a romex cable and put these conductors in the conduit.
I think this is ok but not sure about the ground. I'm aware of the fill requirement. |
Follow-Up Postings:
|
- Posted by circuitbreaker (My Page) on Sat, Jun 16, 12 at 21:14
| If you use a metal conduit you have to use individual conductors (THHN/THWN) as the Romex wires are not rated to be used outside the sheath like that |
|
| Thanks. Can I use romex if I leave in the sheath? |
|
- Posted by circuitbreaker (My Page) on Sun, Jun 17, 12 at 4:15
| Yes you can but it will harder to pull through the conduit and you may have to use a larger conduit or derate the conductors |
|
- Posted by mike_kaiser (My Page) on Sun, Jun 17, 12 at 10:31
| With some exceptions, the metal conduit serves a the equipment ground so there is no need for a ground wire. In that scenario you need to use self grounding devices in firm contact with the metal junction box or use a short pigtail from the device to the box. Of course, if you are a belt and suspenders kind of guy, you can run a separate ground wire and treat it like you would with non-metallic cable. |
|
| "strip the outer jacket of a romex cable and put these conductors in the conduit. " The individual wires in NM are not marked as to type, so they may not be used for other purposes. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.