Lamp Post

parkplaza
13 years ago

Bought a lamp post to replace a 40 year old one that is not working. My husband found a piece of green garden hose from the basement running underground to the lamp post with a cheesy black lamp cord type of wire inside it as the electric wire. Go figure. It was installed so close to the surface, it worked it way to the surface and was run over by a lawnmower and chewed to bits.

The lamp post we purchased did not have instructions. So after doing research there are many conflicting methods...use concrete, do not use concrete. Well, our plan is to install a 22 inch hole filled with gravel on the bottom and then filled with concrete to secure the post. In regards to the electric, we plan on using # 14 outdoor direct buried wiring because the wiring for the light (switch and wall wiring is # 14). The run is about 75 feet in total. We plan on drilling a hole between the joists to get outside. And then use that grey conduit you find in the home stores and install all the way to the post and make a 90 degree bend up into the bottom of the post. We are thinking use direct buried wire for added protection, does this make sense?

Now, in regards to the lawn, we can rent a 3" trench machine for 4 hours for $75 and make the trench. We can either go across the lawn or under a paver walkway from the post to the basement. Is under paver walkway a bad idea? It would avoid the grass damage issue. I was thinking pull up the center pavers, trench, backfill, and replace the paver. How did would you go?

Comments (10)

  • DavidR
    13 years ago

    If you're running conduit all the way, you only need THWN wire, not UF cable.

    You could direct-bury the UF without conduit (except for protection where it emerges from the ground), but you'd need to provide GFI protection at the house.

  • parkplaza
    Original Author
    13 years ago

    Thanks. What about the paver walkway...is that doable to install underneath. Is the grey 3/4" conduit heavy duty enough to support foot traffic if buried 18" or so?

  • brickeyee
    13 years ago

    The Non-metallic conduit is fine under pavers for foot traffic.

    I routinely use rigid conduit so that the depth only needs to be 6 inches.

    A good labor savings for trenching, even with a ditch witch.

  • parkplaza
    Original Author
    13 years ago

    Wow, 6", that is a savings. Thanks a million for the advice. My husband can do that by hand and save on the headaches of picking up returning with the rental (but I will not tell him I said this).

    Can the 6" depth also include the paver bed materials? I believe it is sand. Or do I need to go below that setting material into the actual "dirt?"

    When you say rigid conduit, you are talking the shiny stainless steel conduit, correct?

    We installed the lamp post yesterday and used the plastic grey conduit and stubbed it out outside the concrete pouring (in the hole we made). Can I connect the metal to the plastic? The plastic is 3/4", but I think we may have oversized it from reading other posts. Can we connect 3/4" plasic to 1/2" metal? Is all the metal piping waterproof like the plastic which gets glued?

    I think we will go with the 6" over the 18".

    According other other poster, we will need to return the UF wire and get THWN.

  • mowers
    13 years ago

    Similar conundrum as me. Had a direct buried cable that would not work, so am going to use conduit. I think the PVC stuff seals better. I envison the metal getting rusted and corroded. I think stainless would be cost prohibitive. I think the shiny stuff in the home centers may be for interior use?

  • brickeyee
    13 years ago

    "Similar conundrum as me. Had a direct buried cable that would not work, so am going to use conduit. I think the PVC stuff seals better. I envison the metal getting rusted and corroded."

    Underground is a wet location by definition.

    I think you are thing if EMT (Electrical Metallic Tubing) and not rigid metal conduit.

    Rigid metal conduit goes together with pipe threads.
    It is about as tight as you will get.

    The steel is thick enough and zinc plated so that only very corrosive locations are an issue.

    "Can the 6" depth also include the paver bed materials?"

    Yes, and your AHJ may even allow the pavers themselves.

  • mowers
    13 years ago

    Thanks for the info. That answers it then, the home centers sell EMT and not rigid metal conduit. The stuff was no where near almost a 1/4" thick. I will need to check the electrical supply store, I am sure they have it. Is it expensive? I guess I will need a pipe threader too.

  • pete_p_ny
    13 years ago

    I was reading the lamp post posts being I need to install one too. In Home Depot by me, they sell both EMT and Rigid. The Rigid sections are:

    $12.19 for 1/2"
    $13.76 for 3/4"

    It is not cheap when you compare it to a section of plastic a tad over a buck.

    Plus you need a pipe bender and threader and couplings. There are fittings for plastic that will give you male thread you can install the rigid too, but no clue if this is code approved. There are numerous fittings you get get any configuration you essentially need. I would guess the plastic is a ton easier to use and install plus it appears very forgiving (would bend on a straight away).

    I am not sure if you can install UF inside conduit. I am sure it will work fine, but I think it gets derated?

  • tom_p_pa
    13 years ago

    So what is the verdict....rigid, pvc, or direct buried?

  • brickeyee
    13 years ago

    "Plus you need a pipe bender and threader and couplings."

    Rigid is bent with power equipment, you are not going to bend it with a typical EMT hickey.

    Pre-formed 90 degree bends are easily available.

    You can even escape threading with mechanical connectors (though it uses the same threads as plumbing pipe).