220 circuit. Can I make sub panel?

Posted by joppelt (My Page) on
Mon, Jun 11, 12 at 17:25

A shed has a 220 outlet. (50 amp at breaker box in house.)

I want to put that into a sub panel in the shed, and then feed the original outlet with 220 with its own breaker, but also put a 110 20-amp circuit off that for lights and regular outlets.

Is this kosher?


Follow-Up Postings:

 o
RE: 220 circuit. Can I make sub panel?

You need a 4-wire feed to connect a sub-panel, hot-hot-neutral-ground.

A 240 V load only requires a 3-wire connection, hot-hot-ground.
If the load was 120/240 V (and not a range or dryer) it should have a 4-wire feed.

Otherwise you need a new feed with 4 wires.


 o
RE: 220 circuit. Can I make sub panel?

A lot depends on how the original installation was done.
If it is an underground feed to the shed:
The cable (or conduit) from the house must have four conductors: Two hots, a neutral and a ground. The neutral and ground must be kept electrically separate from the main panel to each load.
It must also be the correct type of cable (probably UF) or wires (THWN).
The size of the wire depends on the length of the run as well as the total amperage.


 o
RE: 220 circuit. Can I make sub panel?

you will also need to drive a ground rod (or drive 2 at least 6' apart so you don't have to worry about ohms)


 o
RE: 220 circuit. Can I make sub panel?

Thanks for the replies.

Actually, I don't know if it's underground or not. Shed backs to the house. It's all old work from a previous owner. And it's all enclosed in walls. My approach is to assume that the wiring is legit, and I was just wondering how to take what I had and wire up a circuit box to split off a 20-amp circuit for lights and outlets.

But it's a 3-prong plug, so I'm assuming 3-wire feed, and from what folks have said here, I can't feed that into a box and split something off.

All the other factors could be 100% perfect, but this makes the idea a non-starter, I guess.

And yes, I know I can run a whole new circuit to there. Other issues make that complicated.


 o
RE: 220 circuit. Can I make sub panel?

For clarification, is this shed a detached building?


 o
RE: 220 circuit. Can I make sub panel?

My question isn't about the shed. That's just where the outlet is. My question is about the outlet, and what I can (not) do with it. My question would be the same if the outlet were in my basement, or in my utility room, or in my bedroom.

And I think we've established that I cannot do what I want to do.


 o
RE: 220 circuit. Can I make sub panel?

Your question might be the same but the location of the shed determines how to correctly and safely wire a sub panel. Electrical mistakes can have catastrophic and sometimes deadly consequences. The folks here just want to make sure you do it right so no one gets hurt.

If you don't have four wires a sub panel is out but you could re-purpose the existing 50 amp, 240V circuit into a single 20 amp, 125V circuit that you could use for lighting and general use receptacles. Would that help you?


 o
RE: 220 circuit. Can I make sub panel?

And that's why it makes a difference.


 o
RE: 220 circuit. Can I make sub panel?

Mike -- I was hoping to preserve a 240 outlet, just for future use. (AND have a lighting/outlet circuit tapped off of it.) That's why I was looking to put it to a sub-panel. But since it's not 4-wire, it's kind of all-or-nothing now on the sub-panel idea.

Without the neutral wire, how would I drop it to 125? Seems like I would have the same problem as the sub-panel (unless I rewire something at the current breaker box, I guess.)


 o
RE: 220 circuit. Can I make sub panel?

For a straight 220 load you use a 2 wire with ground. The white is remarked black and used as a hot. In your case you will take the remarked white off of the breaker, mark it white and use as the neutral. The remaining black will go on a single 20 amp breaker


 o
RE: 220 circuit. Can I make sub panel?

"My approach is to assume that the wiring is legit..."

NEVER assume THAT!!! In fact, assume exactly the opposite!


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here