Homeline Surgebreaker Question

Posted by gardug0213 (My Page) on
Sat, Jun 16, 12 at 13:37

I have a Square D Homeline 200A panel. I just installed an in-panel Homeline Surgebreaker [HOM2175SB] on the top right 2 breaker positions [#2 & #4] with the neutral at the top most position on the nautral bar located on the right side of the panel. My question is, this panel has 2 neutral bars [left and right side]. Would there be a need for 2 Surgebreakers [one on each neutral bar], or is the single Surgebreaker giving me adequate coverage on circuits attached to both neutral bars.


Follow-Up Postings:

 o
RE: Homeline Surgebreaker Question

No. One will do it. The neutral/ground bars are pretty strongly bonded together out of necessity. The instructions for the device do recommend keeping the connecting wire as short as possible without any sharp bends.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here