Posted by nebb (My Page) on
Wed, Jun 22, 11 at 12:31

Have 100Amp breaker below meter (new barn installation) need to run 60 foot underground in conduit to 100amp panel in barn. Want to make sure I install the right size wire to handle and I would rather use copper. First recommendation was #2 stranded on all three wires, Second was #3 for mains and #4 for neutral. Which, if either, is correct? Thanks


Follow-Up Postings:

 o
RE: Wire Size from Meter

Depends on the type of wire (specifically the insulation) but most of the copper you're going to come across (other than UF) is going to be OK at #3 for 100A. You need a ground (which can be #8). What size the neutral is going to be depends on the loads involved. I'd use #3 unless you're guaranteed that you can use otherwise.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here