Tue, Jun 14, 11 at 12:06
| Is there an equivalent to 14/2 UF that is stranded? If so how is it designated? |
Follow-Up Postings:
|
- Posted by mstr_electrician (My Page) on Tue, Jun 14, 11 at 13:55
| No there isnt an equivalent thats stranded. What can be done is install non-metallic rigid conduit(electrical pvc) in the ground at the required depth(24" from grade to the top of the conduit meets all requirements) and use THHN instead of a sheathed cable. Both ends of the conduit must be terminated into a box such as a Bell box. |
|
- Posted by don_1_2006 (My Page) on Tue, Jun 14, 11 at 14:09
| Okay thanks. |
|
| Given that you specified UF, it implies a wet location, and therefore you need THWN. Most wire is rated both THHN and THWN, but it always pays to check. |