GFI/fridge link

Posted by tbass (My Page) on
Tue, Jun 1, 10 at 11:38

We just had a home inspection done (home is for sale). Home inspector claims that our kitchen fridge (tied into a 20A countertop GFI which in turn is tied into its own 20A c/breaker on the main panel)needs to be put on its own c/breaker. The house was built 11 years ago and this set-up was approved by the township electrical inspector at that time. That being said, our basement is completely finished in drywall (ceilings too). Can an electrician re-wire this sitaution without having to tear-up the drywall?
Thanks to all who respond!


Follow-Up Postings:

 o
RE: GFI/fridge link

First off, there's nothing code-wise that prevents the fridge being plugged into the small appliance circuit.

Some might recommend putting it on a non-GFCI circuit as fridges can sometimes trip the things but if it hasn't been a problem, I'm not sure I'd mess with it. While it's possible it could be no drywall cutting, probably some will be required.


 o
RE: GFI/fridge link

Home inspectors are a joke. Tell him to give you the NEC article that states that it must be on it's on circuit and then laugh in his face when he says "What's an NEC?"

I can't stand 99.99999% of home inspectors. They don't have a clue what they're talking about.


 o
RE: GFI/fridge link

It passed inspection when installed. Thank the "inspector" for his/her input and forget about it. If a potential buyer lets this issue prevent him/her from buying they didn't want your house anyway.


 o
RE: GFI/fridge link

Demand your money back. This inspector is a joke.


 o
RE: GFI/fridge link

The inspector is supposed to alert you to possible issues. If you read the official recommendation, it will always say "blah, blah, blah should be checked by an electrician." Home inspectors have to operate in CYA mode 100% of the time.

Depending what else is on the circuit, it may or may not be a problem. If you have lived there for years and it basically never trips, then it obviously working fine as is. If you are constantly resetting the thing, then yes, you should have a separate circuit.


 o
RE: GFI/fridge link

"The inspector is supposed to alert you to possible issues."

Creating issues with bogus references to non-existent requirements does not extend to "possible issue."

All the fool had to say was the the refrigerator was 'noted on the counter circuit' and that it 'could be an issue.'


 o
RE: GFI/fridge link

"All the fool had to say was the the refrigerator was 'noted on the counter circuit' and that it 'could be an issue.' "

Well, we don't really know what the "fool" put in his report. I would be shocked if he definitively commented on a course of action.


 o
RE: GFI/fridge link

Very simply, I would never have a refrigerator on a GFCI circuit. Don't care who approved it!


 o
RE: GFI/fridge link

From the OP:

"Home inspector claims that our kitchen fridge (tied into a 20A countertop GFI which in turn is tied into its own 20A c/breaker on the main panel)needs to be put on its own c/breaker."

Sure sounds like a recommendation/action required.

A refrigerator that is used on a daily basis is not that much of a problem on a GFCI circuit.
Any loss of power is going to be noticed very quickly.

The ones that ARE just dumb are freezers in unfinished basements that are now required to be on GFCI protected circuits.

Go down after a few days to find the contents thawed when the GFCI tripped days ago.

It can be very expensive if the freezer was full.


 o
RE: GFI/fridge link

"Very simply, I would never have a refrigerator on a GFCI circuit. Don't care who approved it!"

Do you do any commercial work?


 o
RE: GFI/fridge link

"From the OP: " - well, this wouldn't be the first person to overreact to a note in an inspectors report. I have a feeling that if the actual report was posted, the inspectors comments would be phrased very similarly to the warning you suggested.

"A refrigerator that is used on a daily basis is not that much of a problem on a GFCI circuit. "

I agree.... until you go out of town for the weekend. It isn't a huge risk, but if given the choice, I think everyone would like the frig on a separate non-gfci circuit.


 o
RE: GFI/fridge link

I agree with not putting the fridge on a GFCI circuit.

The newer GFCIs are getting better are nuisance trips from motors, but it is still not worth the risk.

The inspector is just like many of them, a little knowledge.

Just enough to be dangerous.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here