| Another shed question.
My girlfriend bought a house with a detached workshop/shed. The shed had existing electricity but doesn't connect to the house in any other way (no phone, no pipes, etc.) The existing wiring in the shed had several things wrong (including a single cartridge fuse shutoff with about 5 circuits all wired into it!) So I ripped all that out, installed a 6 breaker subpanel with separate ground bar, etc. I'm pretty skilled with wiring. My Uncle was a licensed electrician and when I was in high-school I wired our house when it was built. (My Uncle would come on Saturdays - inspect my week's work and give me lessons for the next week's work). Here comes my question... The existing underground wire from the house is only a 12-2 NM. That is wrong for two reasons. NM vs UF (see other recent discussion). But the 12-2 doesn't have a ground. So now I have a subpanel without an equipment ground. We are planning on replacing the underground wire at some point (with something bigger and with a ground), but in the meantime, I'd like to ground the subpanel. There are no water pipes, etc. in the shed. Can I install a ground rod at the shed? |
Follow-Up Postings:
|
| As you stated, you have the wrong type of cable and not enough wires. Go ahead and replace with 6/3 w/g UF (or three #6, one #10 THWN in conduit), run a 50A circuit to the building, and separate the neutral and ground. You still need the ground rods. As it is, all you have a 20A 120V feeder. If you were still working under pre-2008 codes, you could bond the neutral and ground at the subpanel, install a ground rod (or two) and be OK, but you only have 20A to work with and only every other breaker in your panel will work (unless you jumper the two legs). |
|
| Thanks. We're planning on replacing the underground cable (with exactly the size you suggested), but money is an object right now. 100ft of 6/3 w/g UF runs into serious coin. The ground is too rocky and uneven to use conduit. We're in New Hampshire. I've already jumpered the two legs in the subpanel. All we have are single pole breakers (three 20A; three 15A) and we're careful about only using one tool at a time. We'll try to win the lottery but until then I'll pick up a ground rod. |
|
- Posted by spencer_electrician (My Page) on Sat, Jun 26, 10 at 2:32
| The ground rod will do nothing unless you bond the neutral and ground together in the sub panel. The white in your feed will be serving both neutral and grounding functions. |
|
| If the ground is rocky, then you'll need to screen the backfill if you use direct burial cable. You don't want those rocks poking holes in the cable jacket. If your existing buried NM is old enough that it doesn't have a ground, it may be about on its last legs. I've pulled up buried NM with ground where the jacket was literally peeling off. That NM had failed shorted in a lightning storm - a surge finished it off. |
|
| If the shed is not attached to the house in any way (structural or any metallic connection except the wiring feeding it power) it is treated as a separate structure. It will require a grounding electrode system even if fed with a four wire service. The now banned 'Worm Getter' relied on this. The problem is that people trying to gather the worms often failed to disconnect the electrodes and got electrocuted trying to pick them up. Sub-panels in separate structures look a lot more like a main panel, since that is what they actually are FOR THAT STRUCTURE.
|
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.