| I've just bought an apartment and am renovating it. Just started on the electrical wiring and have a question.
At the main fuse box, I'm receiving 3 wires that enter the apartment - line (220AC), neutral and ground (presumably connected to the grounding installation of the entire building). There is a main GFCI breaker with the rating of 40/0.5A and a separate GFCI breaker for the bathroom with the rating of 25/0.03A. The apartment piping has been replaced and is now plastic. The bathtub i also plastic. My question is - do I have to ground the metal faucets that connect on the end of plastic piping? Can these anyhow turn out "hot" since they are not connected to metal piping? For instance if a lightning strikes near the building (or onto the building itself) can a dangerous charge accumulate in the faucet and then discharge itself when I (or someone else) hold it? The second question relates to the following hypothetical situation:
|
Follow-Up Postings:
|
- Posted by manhattan42 (My Page) on Sun, Jun 27, 10 at 6:59
| "do I have to ground the metal faucets that connect on the end of plastic piping? Can these anyhow turn out "hot" since they are not connected to metal piping?" No and no. "What happens if a hairdryer falls in the water (remember the piping and the bathtub are plastic)? My bet is that the breaker will trip, but the GFCI will not since none of the current "escapes" to the ground (bathtub is basically isolated right?)." Not correct. The GFCI will trip. GFCIs operate by sensing a difference between the current coming into the receptacle and the current leaving the receptacle. The GFCI will trip when this difference is about 6 millivolts. If you are on a grounded electrical system, the equipment grounding conductor of the bathroom circuit grounds the GFCI back to the main panel. "Or do I worry too much and no harm can happen since the piping is plastic? :)" You worry too much because you have no idea how GFCIs and how residential wiring works. Relax.
|
|
| At the main fuse box, I'm receiving 3 wires that enter the apartment - line (220AC), neutral and ground Not correct. You have two hot lines at 110/120 each and a combination neutral and ground. |
|
| "What happens if a hairdryer falls in the water (remember the piping and the bathtub are plastic)? My bet is that the breaker will trip, but the GFCI will not since none of the current "escapes" to the ground (bathtub is basically isolated right?)." Not correct. The GFCI will trip. GFCIs operate by sensing a difference between the current coming into the receptacle and the current leaving the receptacle. The GFCI will trip when this difference is about 6 millivolts. Maybe nothing since without a grounding (3-wire) plug or some pother path to ground the current will NOT be unbalanced (hot not matching neutral through LOAD side terminals). Current is measured in amps (amperes) not volts (or millivolts). To trip GFCI there MUST be another path for the current to take. No path, no current, no GFCI trip. If you then touched the water and provided another path (possible not not guaranteed) the GFCI would trip. That path must be present and be low enough impedance to allow ~6 milliamps to flow in the circuit with the voltage available. |
|
| Posting from Croatia ! |
|
| GFCIO devices work the same everywhere. |
|
- Posted by manhattan42 (My Page) on Mon, Jun 28, 10 at 6:39
| "Current is measured in amps (amperes) not volts (or millivolts)." That is correct. Current is measured in milliamps not millvolts for GFCI trip currents. Sorry for mis-speaking. "To trip GFCI there MUST be another path for the current to take. No path, no current, no GFCI trip." That is not correct. There is no need for an equipment grounding conductor to be present for a GFCI receptacle to trip. GFCI receptacles trip by sensing a current imbalance between the hot and neutral. This imbalance causes a magnetic field to form in a metal ring through which these conductors pass. It is this magnetic field that causes the breaker to trip in the GFCI device...not the presence or absence of an equipment grounding conductor. This is why GFCI receptacles can be used to replace ungrounded receptacles on ungrounded circuits. See Art 406(D)(E)(3)(a) which says when replacing receptacles when no equipment grounding conductor is present that "Grounding-type receptacles supplied through It is not necessary for an equipment grounding conductor to be present for a GFCI to work.
|
|
| "To trip GFCI there MUST be another path for the current to take. No path, no current, no GFCI trip." "That is not correct. There is no need for an equipment grounding conductor to be present for a GFCI receptacle to trip." I did not say a "equipment grounding conductor" was required. If you grab the hot and neutral of a GFCI protected circuit you can be killed if there is not another path that unbalances the current the GFCI is measuring. Current does not ‘pile up’ or ‘collect’ but flows in complete circuits. " is not necessary for an equipment grounding conductor to be present for a GFCI to work. " Very true. It is painfully easy to have the path, but it must be present. A plug in GFCI tester does not work on GFCI devices without a grounding conductor. This is rather basic electrical stuff. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.