Box fill problem

Posted by ecranny (My Page) on
Mon, May 3, 10 at 22:31

I am trying to find octagonal boxes to install luminaires, and according to code, I need at least 4 inch by 1 1/2 inch boxes to accomodate the wiring. I went to HD and all I could find are 3 1/2 inch boxes (but they are marked as 4"). Lowes didn't have any either. Does anybody know where I can get 4 inch lighting boxes?

Thanks


Follow-Up Postings:

 o
RE: Box fill problem

Tell us what you are trying to stuff into this box.


 o
RE: Box fill problem

I am trying to install multiple boxes, some will have a single 14/2 NM cable, some will have 2 cables (1 in 1 out) with internal clamps, 1 will have 2 cables and a bell transformer wires.... I know how to calculate the required box size, and I know that 4 inch by 1 1/2 inch octagonal boxes will be just fine. However, I can't find any 4 inch boxes. All the boxes I can find are 3 1/2 inches across, even though the store label says they are 4 inches....


 o
RE: Box fill problem

Don't worry about what the actual measurement is, the boxes are listed as 4x1.5in... this is a standard "trade size" and the volume is 15.5 cu.in. If the volume of this box is adequate, you can use it.


 o
RE: Box fill problem

Here is an another question. Since Table 314.16(A) of the NEC mentions 4 inch by 1 1/4 octagonal boxes, but nothing smaller, why would HD and Lowes not carry the 4 inch boxes, but only 3 1/2 inch and smaller?


 o
RE: Box fill problem

There are many electrical components that are available in electrical supply houses that are not routinely carried by the big box stores. I'm still not clear why you think you need really large boxes with your modest box fill requirements.


 o
RE: Box fill problem

Octragon boxes and round boxes only come in one size that have seen. The size that fits under a light fixture or fan properly. Anything bigger wuld hang out of the cover.


 o
RE: Box fill problem

kudzu9: I simply wanted to use a box that is listed in the NEC table, it is not that I want a really large one - in fact I want the mid-sized one because the smallest one is too small....

normel: Thank you for the explantion - to make sure I understand correctly, the NEC indicates 4 inches, but in fact this is a 'trade size' and the actual box is 3.5 inches accross (interestingly it is close to 4" diagonally)


 o
RE: Box fill problem

ecranny-
The boxes you buy at Home Depot are code compliant. You just need to know the cubic inches of the box and comply with the box fill numbers for various gauges of wire, etc.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here