Sub-Panel breakers trip on load

Posted by kgbnsf (My Page) on
Tue, May 11, 10 at 22:12

Hello,

I have a sub-panel circuit box in the garage with four breakers. My 20 amp breaker trips immediately when I engage my larger power tools such as circular saw (12 amps), table saw or other similar sized tools. Smaller tools like my drill, sander, fans, lights are okay. The 20 amp breaker should easily handle the larger tools. Suspecting a bad breaker, as a test I tried the other three circuits and they also trip when engaging my larger power tools. Now I am suspecting a panel issue. The sub panel has a 30 amp main on it and is fed by my main house panel. The house panel has two 20 amp circuits (separate phases, linked together) that feed the garage sub panel.

I just bought the home and I am not familiar with the code for feeding a sub panel. Does this sound like a proper setup? Any ideas why this is occurring? Also, as the sub panel is being fed by two separate phases, I presume I can have 220 circuits up to (40,30 amps?) off of that panel?

Thanks.


Follow-Up Postings:

 o
RE: Sub-Panel breakers trip on load

I still suspect the breakers. I have seen the same thing with GE breakers that were unsually shiny.


 o
RE: Sub-Panel breakers trip on load

"The house panel has two 20 amp circuits (separate phases, linked together) that feed the garage sub panel."

If these are the feeders to the sub-panel you have 240 V if they are on separate legs, but only 20 amps of available current on each leg for 120 V use, or a single 20 amp 240 V load.

If the feed is long or the branch circuit long the starting surge can be extended for a 120 V motor.
This can trip the breaker since the surge may be well above 20 amps.

Household breakers are thermal-magnetic.
The thermal portion provides a 'slow blow' for short overloads, while the magnetic trip provides a very fast reaction to short circuit (300%+ of rated current).

Long conductors create more voltage drop, and this can become critical under starting current (2-3x running current).

The voltage drop increases the starting current and the starting time and can exceed the 'slow blow' built into the breaker.


 o
RE: Sub-Panel breakers trip on load

How long are the feeder wires from the main to the sub panel? What size are the feeder wires? I am suspecting a voltage drop issue.


 o
RE: Sub-Panel breakers trip on load

Thanks for answering the 220 question although the wires going out to the garage probably won't support it.

The feeder wires only appear to be either 10 or 12 gauge. I'll need to pull the panel cover off again to see for certain. The line run from main panel to sub panel is only about 40 feet, going underground from the basement and coming up into the detached garage.

An added twist is that prior to my ownership, the dirt basement craw-space was the neighborhood cat toilet. A junction box for the garage circuit is laying on the dirt floor and wires go from there underground into the dirt and down and out. The box is eroded from acid in the cat pee and in some places, the armored cable is completely eroded through and only the wires are left exposed in their plastic wrapper. I haven't had the opportunity to tackle that one yet nor have I seen how bad things are inside the box. It may be playing a role with the current loss theory.

Fixing that whole mess is another problem in of itself as I don't have any room to play with extra wire. The junction box is already on the ground in the dirt. And, they seem to have just run armored cable into the ground but there is conduit coming up in the garage so it must meet up with it somewhere. A mess, but fairly typical for this 1896 home.


 o
RE: Sub-Panel breakers trip on load

"Thanks for answering the 220 question although the wires going out to the garage probably won't support it."

You either have two legs of the single phase 120/240 V service and have 240 volts or you do not.

Wire size does not determine voltage, it only determines ampacity.

Even #30 wire can carry 240 volts, it just cannot support more than about 5 amps.


 o
RE: Sub-Panel breakers trip on load

Thanks. In my comment above, I meant that the wires probably won't support the amperage load that I would like out there... 40 amps. 220 itself should be fine as I know I am pulling in both phases.


 o
RE: Sub-Panel breakers trip on load

any update on the tripping?


 o
RE: Sub-Panel breakers trip on load

No, but I am going to try a replacement breaker just to see. I'll follow-up after I try it.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here