Breaker tripping in circuit with a contact

Posted by richard904 (My Page) on
Wed, May 25, 11 at 19:49

We have a circuit controlling 3 outdoor flood lights on our house in standard Red Dot fixtures. These are controlled by an Intermatic T101 timer. The timer also controls the outdoor lights for our garage which are on a separate circuit. When the timer signals on, the garage lights work, but the breaker for the house light trips. I presume when the Intermatic timer signals on, a contact is set, and the house light circuit activates. This timer itself will not support two separate circuits. Our breaker panel shows a breaker for the timer and a separate breaker for the house outdoor lights.

What systematic testing would you do to find the problem?


Follow-Up Postings:

 o
RE: Breaker tripping in circuit with a contact

Is this a recently-developed problem in an installation that previously worked OK? Or is this a botched job that never worked properly?


 o
RE: Breaker tripping in circuit with a contact

"This timer itself will not support two separate circuits."

That is exactly what you have described though.

Two circuits, one timer.

Something is not wired correctly, and you could even have 240 V on the circuit that keeps tripping.


 o
RE: Breaker tripping in circuit with a contact

Since we bought the house in 2007 these lights have worked fine on both the garage and on the house. I talked to Intermatic about the T101 and this model will not support two separate circuits. I just presumed that when the timer went on, it sent power to one relay/contact which activated and turned on the house flood lights, and I presumed the circuit the timer was on was the circuit the garage flood lights are on. This makes up the two circuits controlling the flood lights. The garage itself has two other circuit breakers for its ordinary lights and for the 20 amp plugs. Thus this all has worked for a long time until just recently.


 o
RE: Breaker tripping in circuit with a contact

"I just presumed that when the timer went on, it sent power to one relay/contact which activated and turned on the house flood lights, and I presumed the circuit the timer was on was the circuit the garage flood lights are on. This makes up the two circuits controlling the flood lights."

I cannot recall seeing timer that is wired as you have described.

Most have a single hot input line for the timer and the output that is controlled.

When the timer closes the circuit it pulls power from the single hot input and supplies it to the output.

The neutral connections are made around the timer.
One for the timer so it can operate, the other to match up with the switched output from the timer for the controlled circuit.


 o
RE: Breaker tripping in circuit with a contact

My first response was based on the fact that we do not have enough information. That is still the case. The only way a single pole timer switch can properly control loads on multiple circuits is for the timer to operate a multi-pole relay or multiple relays. Is there a relay in the hookup somewhere between the timer and the loads? Anyone made any changes inside the electrical panel from which these circuits originate? And who determined that these loads are on separate circuits? How did they determine this?


 o
RE: Breaker tripping in circuit with a contact

It sounds like someone used a relay to operate the house lights. This relay may have developed a defect that couples the coil to the contacts.

This would be an unusual defect - but the way this system is wired is quite unusual. Baroque, even.

Wild guess, but it suggests an installation done by someone with a moderate amount of electronics experience, and very little home wiring background.

Perhaps I'm missing something, but I don't see any reason not to just remove the house lights from their separate circuit and connect them in parallel with the garage lights.


 o
RE: Breaker tripping in circuit with a contact

davidr: If we connect the house lights with the garage lights, and the short circuit is in the wiring between the house lights, then would I not trip the other circuit breaker? I think this arrangement was done from day one by the original electrician, and the whole purpose was to use one Intermatic timer to control all the outdoor flood lights, and for some reason two circuits were used. The Intermatic timers like the T101 are so cheap, they could have used two timers so the garage flood lights were on one and the house flood lights were on another. By now it is probably time to stop speculating and at least get an electrician out for one hour to tell me what was originally done - I am curious, and then either get a test procedure to fix the problem and restore the house flood lights or make a new installation.


 o
RE: Breaker tripping in circuit with a contact

"a test procedure to fix the problem "

You will not find a "test procedure" anywhere for a job like this.

You have to look at what is there, understand it, then figure out what is wrong.

This is not like debugging electronics.


 o
RE: Breaker tripping in circuit with a contact

Makes me wonder it this timer isn't a 2-pole unit, like for a water heater. They look the same on the surface but there is an extra pair of connections.


 o
RE: Breaker tripping in circuit with a contact

"Makes me wonder it this timer isn't a 2-pole unit, like for a water heater."

There is no reason to bother with a 2-pole timer for a WH.

Opening either leg will turn of a 240 V circuit.

At least Rheem finally realized this also.

I have a Rheem condenser that uses only a single pole relay, and it has far better contacts than the typical ones seen on high current 240 V contactors present in many brands of condensers.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here