Outlets stopped working

arkie62
12 years ago

Two outlets on a circuit with other outlets and some overhead lights just quit working after 6 years. The circuit breaker is good and occasionally I'll get a reading of 120v on both, but as soon as a load is applied to either of the outlets they go dead. I've replaced both outlets with new ones and it has had no effect on the situation. The one outlet feeds off the other, but even if I leave the slave unhooked it makes no difference. I'm no pro when it comes to electricity, but this has me totally baffled. Any suggestions would be appreciated.

Comments (9)

  • randy427
    12 years ago

    It's probably a bad connection at the device, on the same circuit, before the inoperative ones. Perhaps a loose wire nut or screw.
    If you have the type of devices where the wires are inserted in the back and held by a spring-loaded clip rather than a screw (called back-stab devices), these are notoriously failure-prone, resulting in bad connections, and I recommend replacing them all.

  • Ron Natalie
    12 years ago

    I agree with Randy. I'd check the connections on the devices that aren't working and then on the ones that are (starting with the one that appears closest to where you are).

    The 120V reading on the nonfunctional circuit is a phantom. Your meter is very high impedance (it only draws microamps) and is picking up induced currents in the run of disconnected wire there.

  • brickeyee
    12 years ago

    "The circuit breaker is good and occasionally I'll get a reading of 120v on both..."

    You need to be aware of the shrotcomongs of the differnt meter & measuring devices.

    Digital meters put such a small load on the circuit they are prone to 'phantom' voltages.
    The 'non-cpmtact' type probes (light sup when voltage near) are also prone to this.

    Zolder analaog meters are generally the most reliable, though they often lack the bells and whistles of nwere digital meters.

    One thing that often works well is to place a load from a light bulb on the circuit, THEN measure.
    The bulb provides a low enough impedance that phantom voltages are 'bled off' and will no longer affect the reading.

  • arkie62
    Original Author
    12 years ago

    Weird, just another example of a novice not reading the instructions. I had replaced the first device in line, (obviously an old device gone bad, with a GFCI. Didn't pay attention to the fact that it needed to be wired in a specific manner. After much gnashing of teeth and trying everything I could think of, I finally read up on the GFCI device and after finding the hot wires with a homemade light bulb tester as brickeyee suggested, I have everything working again. Lesson learned. Thanks to all of you.

  • Ron Natalie
    12 years ago

    Oh, an another example of not giving us all the information. If you had told us you had been playing with the wiring we might have given you more direct instructions. Always best to confess your sins either here or to the electrician you call in for help.

  • arkie62
    Original Author
    12 years ago

    How do you think I would replace the outlets if I hadn't been "playing" with the wiring. Confess my sins? Learn to read...

  • kurto
    12 years ago

    Replacing outlets does not imply "playing" with the wiring. It is quite common to replace outlets without changing any wiring whatsoever.

  • Ron Natalie
    12 years ago

    He said he outlets "suddenly" stopped working. He mentions he replaced the outlets but that was in the course of "trouble shooting" the failure. He later says that he miswired a GFCI which caused the failure. So the failure didn't suddenly occur, it occured subsequently to him doing improper wiring work.

  • groundrod
    12 years ago

    "and now you know the rest of the story."