Grounding metal gas lines

Posted by coolvt (My Page) on
Tue, May 26, 09 at 18:15

I recently had a gas heater installed in my fireplace. I am on natural gas and all of the piping is black steel. The installer said that the gas lines have to be bonded to the water lines (which are grounded).
A friend had the same heater installed and a electrician ran a ground wire from the gas pipe to the breaker panel.
Is either method acceptable to use?
Mark


Follow-Up Postings:

 o
RE: Grounding metal gas lines

Article 250.104 (B) Where installed in or attached to a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means.

So if it's required to be bonded, a random water pipe is not legal. Metal water piping are required to be bonded always. Gas pipes are only required to be bonded if they may be come energized. If the heater has an electric control system, I'd consider that as something that is likely to energize it so you could use it's grounding conductor or run one back the building ground rods, service enclosure, or service ground connection.


 o
RE: Grounding metal gas lines

Ronnatalie, using that logic wouldn't bonding gas pipes be code, most all gas devices use electricity as well?


 o
RE: Grounding metal gas lines

However the bonding means can also be the equipment grounding conductor of the appliance itself. If you have a gas furnace/dryer/range etc... that is connected to a grounding conductor then the lines are bonded by that connection.


 o
RE: Grounding metal gas lines

Yes I agree with JMVD.


 o
RE: Grounding metal gas lines

"...wouldn't bonding gas pipes be code, most all gas devices use electricity as well?"

"The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means."

It IS BONDED by the equipment grounding conductor supplying power for the devices, and does NOT require any other bonding line.


 o
RE: Grounding metal gas lines

It should be noted that many gas companies are now requiring the gas piping be bonded to the grounding electrode system with #6 Cu if any corrugated stainless steel tubing (CSST) is used within the structure. The idea is to protect the CSST from damage due to an indirect lightning strike. While not an NEC issue, they can and will refuse to turn the gas on until you comply.


 o
RE: Grounding metal gas lines

Normel and others...when I posted the question originally that is the one fact that I omitted. In both cases I dealt with there was corrugated steel tubing involved.
So when you say "bonding to the grounding electrode system" do you mean that it can be bonded to a grounded water line? This is the instructions that a certifed and licensed gas installer gave me.


 o
RE: Grounding metal gas lines

I checked the continuity between the gas pipe and the ground prong on the plug that supplies power to the power vent fan. Sure enough there is continuity so the EGC in the branch circuit is supplying ground.


 o
RE: Grounding metal gas lines

"In both cases I dealt with there was corrugated steel tubing involved. "

The connections made between CST and other [portions of the system are mechanical connections and many use non-conducting material to achieve a seal.

A problem then occurs if lightning induced transients occur on the CST.

It is not effectively grounded and arcing can occur at the connections as the induced voltages seek ground

You have to remember that every conductor in a time varying magnetic field has currents induced.

If the field is strong enough or changes quickly enough the induced voltages can be very high.

Lightning has BOTH large high amplitude magnetic fields AND rapid changes in the amplitude (tens of nanoseconds rise time and thousands of microseconds decay with an overall duration in the hundreds of microseconds to low millisecond range).

Currents can be tens of thousands of amps, resulting in large magnetic fields.

These are the same induced voltages that can damage LAN equipment at hundreds of yards from an actual strike.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here