| I'm adding a subpanel onto my GE TM2020CCU. The subpanel most likely will be a GE TLM1212CCU, for the purpose of feeding four electric baseboards (1500w and three 750 watts), and a water heater.
A GE THQL 2160 60-amp double pole breaker in the main panel
My questions: I plan on using a 4 inch long x 1.25 inch offset nipple between the two boxes. I'll be using #4 THHN to connect the two boxes. Should my ground be #4 BARE or Green? (Can it be #6? Is this a better way to provide ground to the subpanel (as opposed to grounding through the nipple)?
|
Follow-Up Postings:
|
- Posted by ronnatalie (My Page) on Fri, May 11, 12 at 11:25
| Either bare or green is fine. Given the short run, I'd just run a grounding conductor between the two respective ground terminals. You only need a #10 ground here. You only need #6 for the feeder conductors as well. |
|
| Thanks! |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.