Kitchen rope lighting on same circuit as dishwasher or disposer?

Posted by boyler99 (My Page) on
Sun, May 8, 11 at 13:22

Hello,

I am considering installing "rope lighting" along the toe-kick area in my kitchen. I know that I cannot use either of the small appliance circuits for this lighting, but I am wondering if it is permissible to use either the dishwasher circuit (20 amp) or the disposer circuit (also 20 amp)? Neither installation manual for my disposer (InSinkErator) nor dishwasher reference a dedicated circuit being required, and I would be well under 80% of the load of either circuit with this short section of lighting. If this is permissible under the NEC, does the rope lighting need to be on an AFCI breaker? My understanding is that kitchen lighting is still exempt from AFCI but I'm not sure if toe-kick lighting is included in this definition. I am under the 2008 NEC, by the way.

Thanks for the insight.


Follow-Up Postings:

 o
RE: Kitchen rope lighting on same circuit as dishwasher or dispos

It is very unlikely you will have a problem using either circuit.

In many places a single 20 amp (and sometimes just a 15 amp) is used for the GD and GD.

Neither are very large loads, but you can check their nameplate ratings.


 o
RE: Kitchen rope lighting on same circuit as dishwasher or dispos

Per NEC 210.23(A)(2) You cannot add lighting to either appliance circuit if the rating of total utilization equipment fastened in place is greater than 50% of the circuit rating. That will probably rule out the 20A dishwasher circuit if typical @12A rating. But the disposal should be rated well less than 10+ amps. If so, then put the lighting on the 20A disposal circuit.


 o
RE: Kitchen rope lighting on same circuit as dishwasher or dispos

you can check the DW, bot not very many pull 10 amps (50% of a 20 amp circuit).

The lighting does not count towards the 50% limit.


 o
RE: Kitchen rope lighting on same circuit as dishwasher or dispos

Thanks guys, this is very helpful. I think I'll tap off the disposal circuit. Appreciate the assistance.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here