| I need to replace/reroute the 40 foot underground EMT that currently runs from my house to the detached garage. If there is anyone out there can please positively confirm that Sched 40 PVC is/is not permitted instead of EMT, please let me know. I have been unable to find this information anywhere online. Again, I am looking for an answer specific to NYC. Thanks very much. |
Follow-Up Postings:
|
| Contact your city inspector's office for the definitive answer. They'll be glad to answer specific questions like yours. |
|
- Posted by petey_racer (My Page) on Thu, May 3, 12 at 13:09
| Schedule 40 PVC is most certainly allowed underground. In fact it says it right on the pipe. For a "NYC specific" answer you'll need to contact someone in NYC. |
|
- Posted by ronnatalie (My Page) on Fri, May 4, 12 at 10:28
| Does anything (driveway, etc..) pass over the conduit? If so you may wish to consider sched 80 rather than sched 40. Sched 40 is not rated for physical damage protection. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.