sub-panel grounding rod in same structure as service panel?
Posted by jeff_in_lalaland (My Page) on
Fri, May 21, 10 at 5:07
I've hired an electrician to replace a sub-panel in my attached garage. The sub-panel will be bonded via EMT to the service entrance, which is on the outside of the garage -- definitely the same structure. He claims I also have to drive a grounding rod for the sub-panel, and add a GEC from the sub-panel to a nearby water pipe. I don't want to because it costs more, looks ugly, and is likely to confuse future buyers. I can't see any reason for me to do this. Is this a new requirement in the most recent NEC? (I live in Los Angeles)
RE: sub-panel grounding rod in same structure as service panel?
He is 100% INCORRECT.
NO grounding electrode and NO water bond!
A 4-wire feeder is all that is required or wanted.
A 3-wire feeder in a complete metallic conduit system works as well, but the fittings must be made up tight and the bonding on both ends must be correct.
Thanks, Petey_racer
He is not even wrong.
If you DID add another grounding electrode it would need to be bonded to the existing grounding electrode.
This guy is a hack.
A sub-panel in the same structure (including an attached garage) needs a four wire feed.