Kitchen Rewiring

Posted by gpraceman (My Page) on
Sun, May 19, 13 at 1:17

We are starting into a major kitchen remodel and will need to reconfigure the electrical circuits. Fortunately, we have an unfinished basement, which will make it easier to move things around.

1) We are replacing an electric range with a single wall convection oven. The breaker for the range is 50A. The wall oven only requires a 20A breaker, if I read the install instructions correctly. Can I connect the 6 gauge wire to a 20A breaker, or do I need to run a new 12 gauge line?

2) We are installing a gas cooktop and it needs a 15A outlet for the igniters. Can I simply tap off of one of the GFCI protected branches? The install instructions recommend a separate circuit, but that seems a waste for what is essentially a small appliance electrically.

3) Above the cooktop will be a vent hood that requires a 15A breaker. Can I tap into the lighting circuit for that? Or should I just run a new 15A circuit to power the cooktop and vent hood?

4) The dishwasher currently plugs into an outlet that is in the wall directly behind the dishwasher. I thought that the outlet was supposed to be accessible, like inside a sink cabinet. Does this outlet need to be moved or is it fine there?

This post was edited by gpraceman on Sun, May 19, 13 at 1:21


Follow-Up Postings:

 o
RE: Kitchen Rewiring

1) You can reuse the existing wire for the oven.
2) Yes, there is an exception to the "no other outlets" rule for the small appliance circuits for this.
3) If it requires exclusive use of a 15A circuit, you can not.
If it just says it needs to be connected to a 15A circuit, oK, though you may wish to consider a dedicated circuit for it (especially if you've got arc faults on the lighting circiut).
4) depending on how the code is interpretted that MIGHT be acceptable, but having the plug (or other disconnect) under the sink would certainly be preferable.


 o
RE: Kitchen Rewiring

The install instructions for the cooktop says that it is "recommended" to be on a dedicated circuit. I did miss that it says that it will not work properly if plugged into a GFCI protected circuit, so that is out.

The install instructions for the vent hood says nothing about being on a dedicated circuit.

I think that I will just run a new 15A circuit for the vent hood and the cooktop.


 o
RE: Kitchen Rewiring

I will tell you that having just replaced my dishwasher (never again Fisher-Paykel) it was sure convenient having the receptacle readily accessible under the sink.


 o
RE: Kitchen Rewiring

gp
Why do you think the man. says "rec. dedicated cct" ?


 o
RE: Kitchen Rewiring

@laat2 - Doesn't make sense to me. It is a gas cooktop, so the only power is for the igniters. I did find out from another forum that code does allow an exception for the lighting of gas-fired ranges, ovens, or counter-mounted cooking units to be placed on a small appliance circuit.

Anyways, this is my current plan for the appliances:

Gas Cooktop and Vent Hood - Run a new 15A circuit dedicated to these.

Wall Oven - Run a new 20A dedicated circuit for this. Seems better than trying to splice #6 to #12 pigtails. I can move the old #6 line into the cooktop cabinet and terminate it in a junction box there. Then someone who buys the house later on can put in an electric cooktop, if they wish.

Microwave - Move the existing outlet over to the new location.

Dishwasher - Move the outlet into the sink base cabinet.

Disposal - No change.

Refrigerator - Move the outlet to the new location. I'll make sure to check that the circuit is dedicated to the refrigerator.


 o
RE: Kitchen Rewiring

Electronic seigniors do not get along with GFCIs in many cases.

The high voltage to make the spark can leak onto ground all to easily and trip off the GFCI.


 o
RE: Kitchen Rewiring

@brickeyee - I did find a note on that in the install instructions. So, I will not be putting it on a small appliance circuit. I was going to run a new 15A line dedicated to the cooktop and the vent hood.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here