What are the rules on using colored tape to ID wire ends?

Posted by fixizin (My Page) on
Thu, May 6, 10 at 0:16

e.g. if you were to re-wire a whole dwelling with just black and white THWN, what does the NEC/best-practices say about "tabbing" the wire-ends with colored electrical tape?

i.e. how many inches from end, how many wraps, etc.

> Can wire w/ white insulation be used as GND if green tape at each end?

Thanks in advance...


Follow-Up Postings:

 o
RE: What are the rules on using colored tape to ID wire ends?

NEC's position?... anything smaller than #4ga CANNOT be remarked. There are exceptions for multiwire cables, but not for THHN/THWN.


 o
RE: What are the rules on using colored tape to ID wire ends?

I don't think he is remarking wire colours. He is only identifying them at both ends.
Most of the time number markers or wire lablels are used. They wrap around the wrie at both ends so you can identify which is which.

As an example if you had five black wires you could label them 1-5 at both ends.


 o
RE: What are the rules on using colored tape to ID wire ends?

As long as you are simply marking them for identification (not NEC color code) you can do just about anything you want.

There are rules that govern the 're-identification' of wire colors, but most are not allowed in residential wiring with a very few exceptions.

Switch loops should have the white re-marked to indicate it is not a neutral.
You can also re-mark a white as a hot in a 240 V circuit.

Marking a black as a white is not allowed, nor is marking a white as a ground generally acceptable in smaller conductors.


 o
RE: What are the rules on using colored tape to ID wire ends?

Yes, I'm basically asking about using just black for all hot-side conductors, white for all neutrals. Sure it's great to have red and blue for add'l branches in the same conduit, yellow for switch loops, etc., and the whole happy rainbow, but in the DIY quantities I'm looking at, it's a diff between 6.2 cents/ft. and 34.1 cents/ft... no need to work up a spreadsheet on that price delta, lol.

The question about using white as green was just a curiosity, not an issue in my app, which is metal boxes and EMT conduit. The only ground conductors I need are 8" bare pigtails, and that's an easy amount of insulation to strip from solid Cu wire.

Thanks much for the clarifications.


 o
RE: What are the rules on using colored tape to ID wire ends?

Just strip any color handy and use a bare ground.

The only time you would have an issue is if you have an isolated ground in a metal box, and that is not a common thing in residential.

If you are puling into conduit you can use colored tape to mark different circuits.

Just avoid orange. It is used to mark high legs in three phase.


 o
RE: What are the rules on using colored tape to ID wire ends?

No bare grounds in pool/spa wiring either (which you WILL find in residential).


 o
RE: What are the rules on using colored tape to ID wire ends?

"Can wire w/ white insulation be used as GND if green tape at each end?"

NO.

NEC requires equipment grounding conductors size 6awg or smaller to be:

"identified by a continuous green color or a continuous green color with one or more yellow stripes on the insulation or covering, except where bare."


 o
RE: What are the rules on using colored tape to ID wire ends?

Just avoid orange. It is used to mark high legs in three phase.

Check. That must be why my Gardner-Bender multi-color asst. PVC elec. tape blister pack includes just about every color BUT orange. ;')

NEC requires equipment grounding conductors size 6awg or smaller to be:

"identified by a continuous green color or a continuous green color with one or more yellow stripes on the insulation or covering, except where bare."

Double-check. Thanks for the citation. See above.

REALLY don't enjoy re-wiring, and wouldn't do it just to upgrade older TW (60C) wire with THWN (90C) conductors, but bloody hell, when a "hot" is a 12AWG blue wire at the panel (15A breaker), and emerges at the first j-box as a 14AWG red, well, that's redneck code-violating intra-conduit splice I will NOT tolerate. No doubt trying to conserve scrap wire, lol. Similar low-IQ "craftiness" abounds.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here