GFI challenge
| | |
Posted by
tim45z10 (
My Page) on
Wed, Apr 28, 10 at 22:58
| I'm installing a GFI I'm putting two wires on the load side. One wire is slightly smaller than the other. When I screw the tightener, I cant get a grip on the smaller wire. Looking for ideas. Thank You. |
Follow-Up Postings:
RE: GFI challenge
| | |
| Just use a wire nut that support three wires. Wire nut the two main wires with a short pig tail then wire to the one side of the GFI. |
RE: GFI challenge
| | |
| the more important question is why do you have two different gauges of wires on the same circuit? do you have 12 and 14 AWG on the same circuit? If so what size breaker is protecting this circuit? If it's not 15 then you have a bigger issue you need to address. |
RE: GFI challenge
| | |
| One is the wire from the original build, 50 years ago. The other is new. I am going to see if I have enough room for a pigtail. |
RE: GFI challenge
| | |
| I am not aware that wire gauges in use today are any different from that of 50 years ago. I was involved in the trade at that time. I have every NEC including 1959 and since. I need more information before offering advice. |
RE: GFI challenge
| | |
| "One is the wire from the original build, 50 years ago." But you have the breaker sized for the smaller wire, right? Which would also mean it was a waste to run the bigger wire. Which also probably means you have a violation by not having a 20A circuit in a bathroom or kitchen. Unless of course this is a different area. I personally don't like the sound of this whole thing. |
RE: GFI challenge
| | |
| must be that kind of wire we used to use back in the day that shrinks with age.... do the right thing, check into it please and don't just slap on the GFI and call it good. Is your house and safety really worth the risk? |
RE: GFI challenge
| | |
| The difference is only .010-.015. Thanks for the suggestions. I pigtailed it and have completed the project. |
RE: GFI challenge
| | |
| "The difference is only .010-.015." Wire diameter? The difference is than #14 is only rated for 15 amps, while #12 is rated for 20 amps. But hey, at least you are insured by your homeowner's policy against your own mistakes. |
RE: GFI challenge
| | |
| I am not a rookie. I know the difference between 12 and 14 just like you do. So stop with the rash remarks. I dont need them. |
RE: GFI challenge
| | |
| Obviously you've found out how to make it work. I think the concern is that if you have 14 gauge wire in the circuit, you should verify that the breaker is only 15A. It isn't a problem you are causing with your fix, but it is a potential problem you uncovered and you should address it. Adding a GFI has made the situation slightly safer than it was, but that is no reason to ignore a possible fire hazard. In the bigger picture, if you see something like that in a house, it should make you suspicious of all the other electrical work the prior owners did. |
Post a Follow-Up
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in.
If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.