Tue, Apr 27, 10 at 21:56
| I was replacing an outlet today and double checked the circuit after turning off the breaker. To my surprise, it showed about 6-7 volts. I traced the wire back to a junction box and checked it from there with the same results. The wire feeding the junction box is a 12/3 and it appears 2 circuits share a neutral. What could be going on here and should i be concerned? |
Follow-Up Postings:
|
| Bet you are using a distal meter. The input impedance of digital meters is so high they can read voltage that is capacitively coupled to a conductor in proximity to a hot conductor. Plug a light into the receptacle and turn it on. The filament will provide a path for the coupled voltage to ground and you will now measure 9 volts. The effective source impedance for the coupled voltage is very high, but the multi mega-ohm input of a digital meter can read it. |
|
- Posted by ronnatalie (My Page) on Wed, Apr 28, 10 at 7:01
| Distal meters? I always use proximal meters. |
|
| Thanks for the response brickeyee. Learning something new every day. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.