I just ordered some electric snow-melting cable that requires 40A/220V GFCI protection.

We have 200A service to our main panel, and there is only one slot left open. We have two C-H subpanels: one (fed by an 80A breaker) was recently installed for a renovation, and the other is older and fed by a 70A breaker. The older one only has 6 breakers in it, and only feeds our 3 A/C units.

So I thought, no problem, I'll put the 40A two-pole breaker in the subpanel for the A/C, since they will never be used at the same time, and the cover has 5 slots/side. However, I take the cover off and the buss does not extend beyond the existing 3 breakers/side. So I wonder if there is a way I can just install a longer buss in the case to accommodate the new breakers, since the case cover can cover 10 breakers (5/side). Of course, then I wonder if there is something in the NEC about what size feed I would need to accommodate more breakers (even though we will not exceed the 70A feed.

There is plenty of space in the newer subpanel, so that is another option: I could put the new double-pole breaker in there, but then would I need to worry about having a 35A load on one circuit when the whole subpanel is 80A? Yet another option is moving one circuit from the main box to the new subpanel, thereby opening up room for the new two-pole breaker (which would be SquareD rather than C-H).

Any advice is appreciated.


Follow-Up Postings:

 o
RE: Subpanel Issues

"I can just install a longer buss in the case "

Probably cheaper to replace the whole panel.

Panel parts are at a premium cost.

A larger cutout box with bus is very likely to be less than the parts (especially since it is likely to be a special order).


 o
RE: Subpanel Issues

Thanks, brickeyee. Not clear if you thought the other options (moving a circuit from the main box) or putting the breakers in the newer subpanel were not practical.


 o
RE: Subpanel Issues

"would I need to worry about having a 35A load on one circuit when the whole subpanel is 80A?"

That depends on what the other loads on the panel are.

Load diversity, as you planned on using with the AC panel, might still be in your favor.
Few circuits are loaded to their ratings anyway and loading past 80% is generally prohibited, but even that depends on the type of load.

Few loads are long term 100% outside of resistive heating.

You also need to use the actual loads, not just the ratings on the breakers.

Adding up breakers means nothing.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here