40A circuit for a 50A rated appliance. Yea / Nay ?

Posted by davidro1 (My Page) on
Thu, Apr 28, 11 at 20:32

Over in the appliances forum someone wrote:
"We currently have a 40 amp line. Do you think this will be adequate based on the specs?"

The appliance specs say:
Recommended Circuit Breaker - 50 Amps (40 Amps minimum)

I don't know what to do about an appliance that is either 40 or 50 (or more) .

Here is a link that might be useful: RE: Frigidaire Induction Range: 50 amp 'Recommended'


Follow-Up Postings:

 o
RE: 40A circuit for a 50A rated appliance. Yea / Nay ?

A household range, rated at 12kW or less, is perfectly fine and legal on a 40A circuit.


 o
RE: 40A circuit for a 50A rated appliance. Yea / Nay ?

It says 40A "minimum", that's all you legally need.

What you don't want to do is up the breaker and leave the existing undersized wire.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here