What is meaning if a GFCI switch tripped and canít be reset?

Posted by linnea56 (My Page) on
Tue, Apr 6, 10 at 15:46

The little red light is on, but when I press the button to reset, it wonít stay in. I checked the main circuit breakers, but they are all fine. Does it mean the switch needs to be replaced? Itís about 3 years old. Itís in a bathroom, and is used mostly for an electric shaver or a curling iron. Not close to water.

Sorry if it's a silly question. I just never had one that wouldn't reset before.


Follow-Up Postings:

 o
RE: What is meaning if a GFCI switch tripped and canít be reset?

It could be a bad receptacle or it could have a ground fault on the load side. Turn off the breaker and disconnect any wires connected to the load side and restore power. Then see if it will reset. If not bad receptacle, if it does you have a ground fault somewhere downstream.


 o
RE: What is meaning if a GFCI switch tripped and canít be reset?

GFCIs go bad and that's what you could be experiencing.

To expand on what Groundrod said, GFCIs can also be used to protect other devices - what's called "downstream." If any of those devices have a fault, the GFCI will not reset. Turn off the breaker and pull the GFCI out of the wall. There will be two wires (hot and neutral, often black or red and white although not always) going into the top of the GFCI, providing power. If there are two more wires (hot and neutral, not a bare or green ground wire) connected at the bottom, disconnect those wires. Cap those off with a couple of wire nuts. Push everything back into the box and screw the GFCI it in place. Then turn the power back on and see if the GFCI resets. If it does, then it one of the devices downstream causing the problem. If not, the GFCI is bad.

If there is only one pair of wires feeding the GFCI, there is (obviously) nothing downstream and the GFCI needs to be replaced.


 o
RE: What is meaning if a GFCI switch tripped and canít be reset?

What about a faulty--even very slight bad--neutral connection/impedance upstream, maybe even at the main panel? Exactly the sort of fault GFCIs are designed to trip for (aside from the appliances/loads plugged into them, of course).

Hasn't the infamous ALuminum wiring from the 1970s caused such gremlins, when the corrosion gets going?

Just a thought.


 o
RE: What is meaning if a GFCI switch tripped and canít be reset?

"neutral connection/impedance upstream, maybe even at the main panel?"

Downstream maybe, but not upstream so much (though newer GFCIs prevent incorrect installation).

A GFCI device measures the hot and neutral current downstream (LOAD terminals of the receptacle) and from the receptacle in the device (if it has one) for balance. Any difference greater than ~0.005 amps trips the GFCI.

Newer models of GFCI receptacles will not reset if the incoming power is incorrectly hooked to the LOAD terminals instead of the correct LINE terminals.

If the device has been replaced in the last few years it could be incorrectly wired.
If it WAS operating and now is not this is very unlikely.

Moisture (bathrooms and exterior) can cause GFCIs to fail.
They are not very ruggedly built (no coating on the electronics inside) so moisture leads to corrosion and failure.

In most cases simply replacing them is the easiest step to fixing the problem.

If the new one works the old one was bad.
If the new one does not work you need to look further.


 o
RE: What is meaning if a GFCI switch tripped and canít be reset?

Thanks for the added input, folks. The switch is fine now...apparently when it rains and moisture gets into one of the outside, covered switches, it affects the inside GFCIs too. When it dried out outside, the inside one started working again. Weird.


 o
RE: What is meaning if a GFCI switch tripped and canít be reset?

The water is providing a path for current to leak and the GFCI is sensing the leakage.

The leakage is only ~0.005 amps (5 milliamps) to trip a GFCI).


 o
RE: What is meaning if a GFCI switch tripped and canít be reset?

In addition, the GFCI induces a small signal on the hot/neutral so that a ground-to-neutral fault is also detected.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here