GFI trips when something plugged in downstream
Posted by frog_gidget (My Page) on
Fri, Apr 30, 10 at 15:24
Hi there,
I searched but couldn't find how to fix this. I have a tiny kitchen, with 2 GFI outlets. One on each side of the kitchen. One side works fine. The other side has a GFI, and one more outlet over my counter top. GFI outlet works just fine, but anytime I plug something into the outlet next to it, the GFI trips. It can be anything at all, and it doesn't have to be turned out to trip the GFI. My house was flipped, but I met the electrician who did the work. He said this was "normal" (clearly, it's not). How can I fix this? What did he do wrong?
Thanks! I'm going nuts without this outlet!
RE: GFI trips when something plugged in downstream
Well, you certainly are right that this isn't normal. An outlet isn't very useful if it goes out the second you plug something in!
As for what is wrong, you don't have a whole lot of places to check. You know it works up to the GFI. That means the problem is somewhere between that and the next outlet. Check to make sure the GFI is installed properly. Buy a new outlet for the non-gfci (very cheap) and make sure it is wired properly.
Not a pro, but sounds like the second outlet is wired as a slave to the upstream GFI. I agree with bill -- buy a new outlet to replace it and install it. Make sure you turn off the breaker first and check both plugs of the outlet with a circuit tester prior to starting. To be REALLY safe, tag the breaker as OFF while you work.
I suspect highly that you do have a ground fault due to miswiring at either the GFCI or the downstream outlets. It's possible that one of your wires that's on the protected side of the GFCI is touching a wire from the non-protected side (or from another circuit).
It's far more likely that the wiring is screwed up than the receptacle is defective.
You need to open the GFCI and check the wiring. There should be connection to the load terminals for the downstream devices. The should be no connection between white and bare wires.
It could as simple as the ground wire is touching the neutral screw on any of the downstream devices.
If the ground and neutral were touching the symptom would be it would trip all the time even without anything plugged into it... Tripping with a load is most likely as I described it.
sounds like the receptacle is moving just enough when being plugged into to cause the neutral and ground to touch each other. try to reset the GFCI after you plug into the other receptacle. if you can reset, something is moving and touching.
"If the ground and neutral were touching the symptom would be it would trip all the time even without anything plugged into it... "
This depends on the age of the receptacle.
Thanks for the helpful advice folks, I opened it up and it seems that they twisted the white wires together and only have one hooked up to the gfi. Any ideas how ti fix this?
Here is a link that might be useful: photo of wires
You need to figure out what white wires go with the downstream loads and remove them from the bunch and connect them to the load side white screw of the GFCI.
Turn off the breaker and check for voltage.
It is probably going to take an ohm meter and an extension cord to chase the wires down.
If you separate all the white wires in the bunch, then plug the extension cord into a downstream receptacle you should be able to figure out the correct white wire for the load side.
Did an electrician do that?
Remove the white connecting to the GFCI. Remove the wire nut holding the white together and untwist the wires. Throw out the short piece of white wire.
You will see the wires are bundled together in a set of black/white/green as the enter the box. Find the white wire that is bundled with the bottom black wire and connect it to the bottom screw on the side where the current white wire is. Connect the other white to the top screw.
Assuming he had the live/black wires in the right slots to begin with, that should work. If not, move the top black/white to the bottom and the bottom black/white to the top.
I can't tell from the picture if the upper set screw on the neutral side is missing. If so, you would just need a new screw.