3- or 4-wire to 120v subpanel in unattached "garage"?

Posted by dcsullivans (My Page) on
Mon, Apr 22, 13 at 15:00

Hi -

We have a storage shed about 100' feet from the house on our property. It has no power now, and i'd like to run some out there so that I can have a couple of flood lights, have an outlet for the weed wacker, the occasional portable saw, etc. I only need a 120v circuit at this time.

I plan to run 1 or 1.5" PVC conduit underground with either 3 or 4 THWN lines (neutral, ground, and either 1 or 2 hots.) I'm thinking of using #10 wire, not so much for the amperage capacity, but to limit voltage drop.

Since I only need 120v, I'm planning on leaving the second hot wire (red) capped off at each end. My thinking is that if I ever needed 240v, I'd be able to upgrade without any additional digging, pulling wire, rewiring, etc.

I'm thinking that I'll install a small subpanel in the shed, but connect only 1 side of the bus. The neutral and ground will be isolated from one another, and I'll install 2x 8' grounding rods outside the shed.

Any thoughts or comments on this plan?

In particular, any reason to connect up both hots to the panel right away, even though I only need two somewhat smaller circuits at this time?

Thanks
Matt

This post was edited by dcsullivans on Mon, Apr 22, 13 at 15:05


Follow-Up Postings:

 o
RE: 3- or 4-wire to 120v subpanel in unattached "garage"?

any reason to connect up both hots to the panel right away

Why would you not hook up both hots? You'll have done 99.9% of the work already, so why not hook it up?


 o
RE: 3- or 4-wire to 120v subpanel in unattached "garage"?

No real reason, other than I have to have a double-pole ready to go at the main panel.

Things are already a little crowded in there, so I might have to do a little juggling.


 o
RE: 3- or 4-wire to 120v subpanel in unattached "garage"

The newest NEC requires 4-wire feeds to separate building panels.

What year NEC is the AHJ using

it is NOT always the latest one.

There is a separate provision that allows a single circuit to feed a detached structure without any panel at all.

20 A is the max, and GFCI protection is required on the feed.

A mutliwire circuit is a 'single circuit.'

This post was edited by brickeyee on Mon, Apr 22, 13 at 19:52


 o
RE: 3- or 4-wire to 120v subpanel in unattached "garage"?

2005 NEC.

I'd rather run the 4-wire than do just the single circuit, even though that's probably all I need at the moment.

Thanks


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here