Need for Laundry room GFI

Posted by stash-hdy (My Page) on
Mon, Apr 16, 07 at 9:35

My plugs in the laundry room are not GFI protected, should they be by code?


Follow-Up Postings:

 o
RE: Need for Laundry room GFI

Don't quote me on this, because I don't know what the latest revision of the code says. But, in the past, most localities have not required GFIs in laundry rooms provided that the washer was the only source of water in the room -- i.e., there is no sink or other source of water. If there is a sink, then the usual rules about outlets near the sink applies.

Washers have in the past been exempt from GFI outlet requirements because of problems with nusiance tripping. I'll admit that I don't know for sure what the NEC says now, but I do know that the inspector did not make me put in one in our just-completed house.


 o
RE: Need for Laundry room GFI

there is no requirement for GFCI protection on the 20 amp required laundry circuit.
Any other receptacles in an unfinished basement are required to be GFCI protected.
The presence of a sink and water has nothing to do with the requirements.


 o
RE: Need for Laundry room GFI

Yes the presence of a sink within 6 feet of the receptacle requires it to be a ground fault protected, and that includes the washer receptacle if it is within 6 feet of the sink. 210.8(A)(7) who said this was in a basement?


 o
RE: Need for Laundry room GFI

What about receptacles in a finished basement. If I have a slop slink between my washer and dryer, and one outlet, does that need to be a GFCI.

Also, a general question, am I required to update everything in my home. IE - My house was built in 1963, and the exterior outlets, basement, and garage are regular outlets. Do I need to replace?


 o
RE: Need for Laundry room GFI

With a very few rare execptions, you are not required to update existing wiring just because the code changes -- as long as you do not alter said wiring. If you change anything, you may be required to bring part or all of the existing wiring up to current code.

A finished basement is treated like any other finished part of the house AFAIK. If the outlet is within 6' of the slop sink -- measured horizontally -- it is supposed to be GFI. If said outlet happens to be the washer circuit, I'm not sure which rule takes precedence. If it were me, I might go ahead and install one anyway if it's an old ungrounded circuit. I think the nuisance tripping problems that the earlier GFIs had has largely been eliminated now.

And yes, I assumed that "laundry room" meant a finished room. My apologies if this is not the case.


 o
RE: Need for Laundry room GFI

Stash-hdy
If the outlets were to code when they were installed, they still are to code and no changes are required unless you wish.


 o
RE: Need for Laundry room GFI

Exactly what hendricus said. Codes are not retroactive.

Besides, the code groundrod quoted is the 2005 NEC quote. This section was added in the 2005 edition. In 2002 this requirement did not exist. So if you have an installation predating 2005, OR if your area is not even yet under the 2005 edition (as MANY are not yet), then no GFI would be required.

Of course it is not a bad idea, it is just not mandatory.


 o
RE: Need for Laundry room GFI

"Yes the presence of a sink within 6 feet of the receptacle requires it to be a ground fault protected, and that includes the washer receptacle if it is within 6 feet of the sink. 210.8(A)(7) who said this was in a basement?"

A sink in a laundry area is NOT a "wet bar".
Want to try again?


 o
RE: Need for Laundry room GFI

I'll try again for you brick, and I'll type real slooow.

210.8(A)(7) states:

Laundry, utility, and wet bar sinks where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink.

It would be that first word that starts with an L. as in laundry sink. As they say around the poker table, read it and weap.


 o
RE: Need for Laundry room GFI

There doesn't seem to be an exception in the code for the dedicated laundry outlet, but a lot of AHJs will let it slide because nothing other than a washing machine will ever be plugged into it, especially if it's *behind* the washing machine. Some like to see a single (non-duplex) outlet and/or a "for washing machine use only" label too.

This appears to have a subtle but important difference from the common debate about whether a dedicated fridge circuit in a kitchen requires a GFI - that argument turns on the AHJ's definition of "receptacles installed to serve the countertop surfaces".


 o
RE: Need for Laundry room GFI

Try typing REAL SLOW and ADDING in the NEC year?


 o
RE: Need for Laundry room GFI

I have a question. We have installed a cabinet, sink, front load w/d, all with a countertop. I was told by a retired electrician that the outlet under the laundry sink, in an enclosed cabinet, used to plug in the washing machine, did not need a GFI. Of course, and outlet above the countertop, near the sink would have to have a GFI. Is this istallation OK with code?

DP


 o
RE: Need for Laundry room GFI

If this is a new installation then the receptacle would likely need GFI protection.

If it is an older existing receptacle then it likely does not require it.

Your "retired" electrician probably is not up on the most recent codes.

The GFI requirements do not, and never did, reference cabinets and counters. Just a 6' distance from a laundry sink.


 o
RE: Need for Laundry room GFI

Try typing REAL SLOW and ADDING in the NEC year?

The person referencing an older NEC is the one who needs to state that.

An undated reference would be assumed by any reasonable person to reference the latest code.

It is extremely unhelpful to simply state older code requirements without any mention of the fact that they have been changed.

The most helpful answer in a case such as this would be to mention that it has changed recently, and state both sets of requirements.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here