| My garage has the builder wiring - one 110V outlet on each wall. Is it advisable to add outlets by running 12-3 around the space and having 2-gang boxes with both 110 and 220 volt in the same box from the same cable?
Thanks. |
Follow-Up Postings:
|
- Posted by bus_driver (My Page) on Sun, Apr 11, 10 at 8:46
| Today the standard voltages are 120 and 240. The measured voltages at individual premises may and will vary slightly. If fed from a double-pole breaker that is common-trip and shuts off both poles with one motion of the hand, the installation you envision is permissible. |
|
| Not really a good idea. Most devices that require 240 volts also require dedicated circuits. Also the 120 volt receptacles require GFCI. If you do it with 12/3 you will require each receptacle to be GFCI or a GFCI breaker. |
|
| It is called a multiwire branch circuit (AKA an 'Edison circuit) and is acceptable if you meet the handle ties rules bus driver listed. Even older versions of the code required a common trip (handle tie) if a device yoke (duplex receptacle strap) had both legs present (upper receptacle on one leg, lower on the other). The regular 120/240 service uses the same method. |
|
- Posted by mike_kaiser (My Page) on Sun, Apr 11, 10 at 10:09
| Without seeing your home it's hard to say but typically a garage would be served by a single circuit. With that kind of setup, you couldn't get 240v. 240v is derived from two hot wires on opposite poles. Even if you have opposite legs available, remember that you are limited by the existing wiring. If you have, say, 14 ga. wire then you can only use a 15 amp breaker (and a 20 amp breaker for 12 ga. wire). If you plan on using any high draw tools, like a welder, you are going to need a new circuit with the appropriate sized wire and breaker. You might be better served by installing a small sub-panel in your garage for your 240v circuits and new 120v circuits. Remember too, that current code requires 120v circuits to be GFCI protected in a garage.
|
|
| Thanks for the responses. The garage has a 150A sub panel or I wouldn't have asked the question, frankly. It already has a 20A 240V branch properly breakered to a single outlet. This garage is a part-time wood shop. Currently have two staionary tools capable of operating on 120 or 240 volt. One is wired for each at present because that's how they arrived. Not sure about the logic of 240V devices requiring individual circuits. Nothing magic about the voltage and the big rule is not to exceed the capacity of whatever circuit you might have. I was thinking to install 12 gauge wire and the saw and jointer each have 15a plugs, and draw around 5.5 amps each. I don't envision running both at once. Am I missing something? My intent in putting them on 240 is to add versatility to the shop and impose some automatic discipline in separating medium draw devices from, say, the radio and battery chargers by putting the power tools on the power tool circuit. Then if I had the 120 also available then I would tend toward using those outlets for lower-draw tools also, like grinder, scroll saw. I could see installing a GFCI in each box as they're not that expensive. Seems to come down to price of individual GFCI's versus the wiring effort and the price of wiring. Since the garage itself is a work in progress I think I'll 1. Think it over for now 2. Add outlets to the existing 120V circuits where appropriate 3. Extend the 240V circuit to a couple convenient spots, and if there is not already a 120V outlet nearby, add a 120V GFCI receptacle 4. Make up a 240V extension cord for the time being. How's that sound? |
|
| Using a 20 amp multi-wire circuit for higher draw 120 V tools works fine. It gives you two separate 20 amp circuits on each duplex receptacle if you want it. It allows the use of a larger router and a vacuum for chip collection without overloading, all you have to do is make sure they are plugged in to the different legs. In my shop all lower receptacles in a duplex are on one leg, all uppers on the other. Any large stationary tool that can be converted to 240 V usually should be. |
|
| Separting devices is a good idea. Your original plan won't do that. They would both be running on the same circuit. The 120 volt devices would use half (one hot and neutral)and the 240 volt devices would use the whole circuit(both hots). That is why I suggest separate 240 circuit not a multiwire circuit with both 120 and 240 devices. If your machines are wired for 120 now you will need to change the plugs when you convert them to 240. |
|
| Brickeye and Bus_driver - thanks for the assistance. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.