basic electrical wiring fix suggestions

Posted by austingardner (My Page) on
Tue, Apr 5, 11 at 0:12

Greetings,
This wall light seems to have over heated and no longer works. I'm not sure why, but when I removed the sconce cover to take a picture of the damaged wires, there was a spark and the breaker flipped. I'm guessing the wire needs to be replaced and I'm wondering how I can go about safely making this repair. Any thoughts or suggestions are extremely appreciated.
Projects with questions
Projects with questions


Follow-Up Postings:

 o
RE: basic electrical wiring fix suggestions

Looks like the bare wire end in the photo is touching the fixture stud, which is fastened to the box. With a grounded box, that would explain the spark. However, with wiring this old, I'd be very surprised if the box were grounded.

The condition of the conductors in the box doesn't look too bad, considering their age. My guess is that if the fixture failed you'll need to have it rewired, or rewire it yourself. Or just replace it. Then, much as I hate to say it, it's time to put that old ceramic wirenut out to pasture and replace it with a new one. I personally like Scotchloks, but I think I'm probably in a minority. Everybody seems to have a favorite.

PS - it's really not a good idea to be working on live circuits. The fact that the breaker tripped may have saved you from a severe shock.


 o
RE: basic electrical wiring fix suggestions

It might not be "effectively" grounded, but stranger things have happened that a metal box wasn't connected to a ground some how.

I'm not sure that a IDC ScotchLok would be real easy or effective on cloth coated wiring, are not UL listed for such, and are hence NOT LEGAL in most jurisdictions.


 o
RE: basic electrical wiring fix suggestions

Do Scotchlok connectors even have a UL listing?

They are not aimed at the permanent AC building wiring market (as in NEC compliant), but marine, mobile home, etc.


 o
RE: basic electrical wiring fix suggestions

The IDC ones do not appear to have a listing that would apply to building wiring. Some of them do have UL listing for other purposes. Confusingly, 3M also markets traditional wirenuts under the ScotchLok trademark, so I don't know which david was technically referring to. The IDC ones as I pointed out are not listed and further won't even work to my knowledge on fabric insulation.


 o
RE: basic electrical wiring fix suggestions

Before you go spending and money:

If the wire popped loose from the wire nut as you removed the fixture, that bad connection could have been the original problem. Take some fine grit sand paper or emory cloth and clean off all the crud on the copper. Securely connect the wires with new nuts and replace the bulb.

It that doesn't work, then the problem is likely in the fixture and it will have to be rewired.


 o
RE: basic electrical wiring fix suggestions

I was referring to Scotchlok wirenuts. I didn't even know they offered IDC connectors.

Here is a link that might be useful: Scotchlok Wirenuts (red)


 o
RE: basic electrical wiring fix suggestions

OP, be very careful in that box.

It appears to be cloth covered rubber insulated conductors.

The rubber insulation may be VERY dry and fall off the wires if they are moved or bent.

The most common fix is some heat shrink tubing, and you can place it over the existing cloth braid and rubber insulation without removing them.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here