30 amp breaker okay for this double oven?

ebiker
14 years ago

We are remodeling our kitchen.

We are replacing the existing single wall oven with a double wall oven. Currently 10ga wiring feeds the oven with a 30 amp breaker at the box. 240V single phase.

Question: an Electrolux double oven we are considering has the following specs:

Power Source:

Total Connected Load: 8.0 kW @ 240V / 6.0 kW @ 208V

Other Requirements: 40 amp grounded outlet

Max. Amp Load: 29,33

Ratings: UL rating

Power Source: Electric

Since the max amp load at 240V is 29 amps, wouldn't my existing 30amp breaker and existing 10ga wire suffice?

Here is a link that might be useful: Electrolux double oven

Comments (8)

  • tim45z10
    14 years ago

    Follow the manufacturers recommendations. Why risk it.

  • joed
    14 years ago

    No big enough. You need a 40 amp circuit.
    8.0 Kw @ 240 volts is 33.333 amps.
    The specs should include a circuit size if read further.

  • brickeyee
    14 years ago

    "Other Requirements: 40 amp grounded outlet "

    Equipment must be installed in accordance with the manufacturer's instructions.

  • bigbird_1
    14 years ago

    "Other Requirements: 40 amp grounded outlet"

    Is the oven 120V/240V, or just straight 240V? That will determine if you need 8/3 or 8/2 cable.

  • ebiker
    Original Author
    14 years ago

    Thanks for the feedback! The specs from that Sears site are backwards it looks like. It certainly would be 33 amps at 240v, so a 30 amp breaker won't work.
    I wish we could run 8ga wire to the oven location, but it's not a possibility. Sure would open up more double oven options for me!

    In my shopping, I'm still surprised that some specs call for a 40amp outlet, even though the calculation of max Amps (Watts divided by Volts) equals less than 30 amps. (ie some ovens are max rated at 6700 watts @ 240v = 28 amps, but the specs still call for a 40 amp outlet.) Is there something I'm missing here?!
    I don't want my 30amp breaker tripping all the time if I'm miscalculating, but it would sure be nice to have some other oven options than what I'm currently looking at.

  • Billl
    14 years ago

    There is a safety "fudge" on electrical rating of 20%. If you are over 80% of the usage rating, they round up to the next standard size. You don't want to put anything on a circuit that is going to continually push right up to the limit.

    "I wish we could run 8ga wire to the oven location, but it's not a possibility"

    Not sure why you say this, but where there is a will (and some money) there is a way.

  • joed
    14 years ago

    Normally there is a minimum 40 amp circuit installed for a stove. Only a separate cooktop or separate oven will use a 30 amp circuit. Combine them into a range or double oven and you will need the 40 amp circuit.