| We are remodeling our kitchen.
We are replacing the existing single wall oven with a double wall oven. Currently 10ga wiring feeds the oven with a 30 amp breaker at the box. 240V single phase. Question: an Electrolux double oven we are considering has the following specs: Power Source: Total Connected Load: 8.0 kW @ 240V / 6.0 kW @ 208V Other Requirements: 40 amp grounded outlet Max. Amp Load: 29,33 Ratings: UL rating Power Source: Electric Since the max amp load at 240V is 29 amps, wouldn't my existing 30amp breaker and existing 10ga wire suffice? |
Here is a link that might be useful: Electrolux double oven
Follow-Up Postings:
|
| Follow the manufacturers recommendations. Why risk it. |
|
| No big enough. You need a 40 amp circuit. 8.0 Kw @ 240 volts is 33.333 amps. The specs should include a circuit size if read further. |
|
| "Other Requirements: 40 amp grounded outlet " Equipment must be installed in accordance with the manufacturer's instructions. |
|
| "Other Requirements: 40 amp grounded outlet" Is the oven 120V/240V, or just straight 240V? That will determine if you need 8/3 or 8/2 cable. |
|
| Thanks for the feedback! The specs from that Sears site are backwards it looks like. It certainly would be 33 amps at 240v, so a 30 amp breaker won't work. I wish we could run 8ga wire to the oven location, but it's not a possibility. Sure would open up more double oven options for me! In my shopping, I'm still surprised that some specs call for a 40amp outlet, even though the calculation of max Amps (Watts divided by Volts) equals less than 30 amps. (ie some ovens are max rated at 6700 watts @ 240v = 28 amps, but the specs still call for a 40 amp outlet.) Is there something I'm missing here?! |
|
| There is a safety "fudge" on electrical rating of 20%. If you are over 80% of the usage rating, they round up to the next standard size. You don't want to put anything on a circuit that is going to continually push right up to the limit. "I wish we could run 8ga wire to the oven location, but it's not a possibility" Not sure why you say this, but where there is a will (and some money) there is a way. |
|
| "There is a safety "fudge" on electrical rating of 20%. If you are over 80% of the usage rating, they round up to the next standard size. You don't want to put anything on a circuit that is going to continually push right up to the limit." You are only allowed to use up to 80% of a circuits load continuously (except for some vary narrow restrictions). An oven is a continuous load since it can pull its full rated power for an indeterminate time. A 30 amp circuit cannot supply a single load of more than 24 amps. A 40 amp circuit is limited to 32 amps. |
|
| Normally there is a minimum 40 amp circuit installed for a stove. Only a separate cooktop or separate oven will use a 30 amp circuit. Combine them into a range or double oven and you will need the 40 amp circuit. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.