Generator load balancing

Posted by Amphicar770 (My Page) on
Sun, Mar 10, 13 at 21:27

Hi All,

Now that I have my generator hooked up via interlock, I have been looking at the watt meters I installed on each of the hot legs to ensure everything is balanced.

Now, obviously the load balance will shift dependent on what is powered up at any given time. What would be considered a normal range of difference between the two legs on a 10kw, 12.5 kw surge, Honda diesel genset.

Thanks.


Follow-Up Postings:

 o
RE: Generator load balancing

As long as each leg is under the maximum supported it is OK...obviously is one side is greatly underutilized you're wasting capacity.

Do you really have a 770? Those are way cool.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here