| Hi. I have two welders, one is a standard 240v/22 amp MIG, the other is an odd 120v/26 amp stick/arc welder.
Would it be possible for me to install a dryer style 120/240v 30 amp breaker (the ones with a neutral), and pigtail/split one of the 240v leads and the ground? Then I'd have three hot wires, one neutral and two ground. I'd take the two hots and a ground and put them into the standard 240/30a plug, and the third 240, the neutral and the other ground into the 120/30a plug. Does that sound like a good idea? Would it be up to code? The other solution is to simply install two breakers. That's not much harder, but I'd like to simplify if possible given that I won't be operating both welders at the same time. |
Follow-Up Postings:
|
- Posted by bus_driver (My Page) on Sat, Mar 12, 11 at 21:29
| The equipment grounding conductor MUST NOT be used as a circuit conductor. Under certain conditions, that can be fatally dangerous. If you add an appropriate neutral, properly installed, the plan is fine. |
|
| A completely different code section covers welding equipment. Article 630 Like motor circuits wire size is no longer directly set by breaker size. |
|
- Posted by mike_kaiser (My Page) on Sun, Mar 13, 11 at 10:04
| My basic reading of 630 says that under certain circumstances wire can be undersized based on the duty cycle of the welder. In a residential setting it might be better to run full sized wire to future-proof the circuit recognizing that the next owner might own a different tool and never look at the wire size. If the MIG welder doesn't require a groundED (neutral) conductor, then you don't need to use a 4-wire receptacle but in this case you would need to pull 3 wire (+ ground) cable or 4 wires in conduit for a neutral required for the 120v stick welder.
|
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.