gfci

Posted by cappo11 (My Page) on
Fri, Mar 5, 10 at 19:18

okay I have a house that is 4 years old. all of a sudden when we turn on the bathroom exhaust ceiling fan the gfci outlet on the wall trips. Even when there is nothing plugged in. If you turn the fan off, you can reset the gfci. I noticed that the entire bathroom is on 1 breaker. could this be the problem? any help would be appreciate


Follow-Up Postings:

 o
RE: gfci

Bathroom on one 20 amp breaker is code. Sounds like you have a faulty fan.


 o
RE: gfci

The fan does not have to be GFCI protected unless it is in the installation instructions.

The fan likely has a defect.


 o
RE: gfci

I should have mentioned that the fan is not gfci protected. The gfci is on same circuit as rest of bathroom but is pigtailed and doesn't control anything else


 o
RE: gfci

The fan is on the LINE side of the GFCI?

Sounds like someone hooked some neutrals together incorrectly.

Other devices on the line side of the GFCI should not have any effect on the GFCI if all the wiring is correct.


 o
RE: gfci

thanks for the help. but sounds like a job for a pro.


 o
RE: gfci

With a DVM and an incand. lamp you can very likely check whether the GFCI is tripping for valid reasons, but the default fix is to replace the GFCI.


 o
RE: gfci

I will change the gfci first, and then the fan motor if there is still a problem. Is it o.k. that the gfci and exhaust fan are sharing a neutral?


 o
RE: gfci

both the neutrals have to be on the line side of the G.F.C.I.


 o
RE: gfci

both the neutrals have to be on the line side of the G.F.C.I.

To elaborate: There needs to be THREE neutrals. The feed from the circuit breaker has one, the exhaust fan has one (those should be connected together either and to the LINE side of the GFCI). Any GFCI protected loads have one and that should be connected to the LOAD side. Nothing form the protected side (hot or neutral) should touch anything on the line side. Also make sure that none of the neutrals touch ground anywhere (other than back at the disconnect).


 o
RE: gfci

thanks ronnatalie for explaining. the wiring is just as you say it should be. looks like I have a bad gfci


 o
RE: gfci

If the GFCI can be reset and everything else works untill you turn on the fan, I don't see how it could be the GFCI.

If the above statement is true then the GFCI is doing its job.


 o
RE: gfci

I installed a new gfci and has been working fine since. Thanks for the help


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here