Return to the Electrical Wiring Forum | Post a Follow-Up

 o
POCO cable upgrades in neighborhood

Posted by grandmum (My Page) on
Fri, Mar 16, 12 at 17:08

The power company in my area is upgrading the wiring between each transformer (pad mount) in my neighborhood. There NOT replacing cable from transformer to homes. Does this mean when they do the work, that everytime they disconnect a transformer in my neighborhood to make the new connection that we will get a momentary power blink.outtage?

Silly question perhaps, just curious what to expect.


Follow-Up Postings:

 o
RE: POCO cable upgrades in neighborhood

Probably. My company did the same thing and the power was out for a few minutes.


 o
RE: POCO cable upgrades in neighborhood

Yeah but it's preferable to when the cable blows at the end of it's useful life. We had some that was in need of replacement. Three or four times the 13KV line to the transformer between my house and my neighbors blew. They'd drive down my driveway, fire up a generator and back feed the cable with a pulse and wander down the street listening for the arc... Then they'd spend a couple of hours digging up the thing, replacing the bad section, and putting the dirt and grass back.

I've got the bad section on one of the failures sitting on my workbench somewhere. Pretty clean hole arced through almost a 1/2" of dielectric.


 o
RE: POCO cable upgrades in neighborhood

So what I am asking if everytime a cable is disconnected and the new cable get connected to the transformer, will I will see a momentary blink? Even if its down the block (NOT the connections on the transformer that feeds my home).

I assumed I would get a blink when they work on my transformer but fear I will see multiple blinks for each new connection at other transformers in area that will reak havok on my electronics multiple/many time during the upgrade.


 o
RE: POCO cable upgrades in neighborhood

Power will likely go out. Not just blink.
Depends on how the subdivision is wired.


 o
RE: POCO cable upgrades in neighborhood

They should have notified you of the date and time
of the outage, along with the duration.
If they haven't, give them a call.


 o
RE: POCO cable upgrades in neighborhood

Unfortunetly no other info from the POCO is available at this time.

Can anyone else speculate on how this process of replacing the underground cable from transformer to transformer might work and how I may or may not be effected by power interuptions?


 o
RE: POCO cable upgrades in neighborhood

If the POCO has not notified you, or your neighbors,
then your power will not be affected. I don't
understand why you cannot contact the POCO.
Let's pretend that your power went out completely,
what would you do, post to a forum?


 o
RE: POCO cable upgrades in neighborhood

I'm with lbpod on this one. I'm not sure what kind of info you are looking for.
If your power does happen to go out, reset your clocks and move on with your life. :)


 o
RE: POCO cable upgrades in neighborhood

If they are simply replacing distribution lines the power vary well may be out for minutes to longer as they connect new lines to the old transformer primaries.

The length of time can be highy variable depending on how the distribution lines are installed initially.

If cable duct with adequate spare space was installed (a rarity except in cities usually) it would be relatively brief.

If they are forced to ditch in new distribution lines (instead of pulling them into existing cable duct) it could be longer. More work has to be done at each transformer than in a typical duct installation.


 o
RE: POCO cable upgrades in neighborhood

They have done this in my neighborhood.

They opened a trench and lay the new cable.

They shut off the power to attach the new cable.

They did NOT notify us (me, at least) when this happened. Power was off for several minutes.

If you have a situation where turning off the power would be harmful (medical equipment maybe), you should call the POCO and let them know about it.


 o
RE: POCO cable upgrades in neighborhood

"They opened a trench and lay the new cable. "

Think how much money they saved over putting in even small cable duct!


 o
RE: POCO cable upgrades in neighborhood

They used a DitchWitch or something similar.

From what I could tell, it seemed that the subdivision was wired using Delta transformer configurations with 2 of the 3 terminals in use. The change was to add the new 3rd cable. But it looked like they also put cable duct down as well.


 o
RE: POCO cable upgrades in neighborhood

"They used a DitchWitch or something similar. "

Pretty large ditch witch to meet the burial rules for even 240 v service lines (they are not covered by the NEC, but have a separate 'code').


 o
RE: POCO cable upgrades in neighborhood

They might not be as deep as you think. Many places have a minimum cover of 30" of dirt over primary or secondary cables. This is for direct buried or cable in duct. Direct bury is foolish in my opinion but many utilities to this day still do it. I would much rather pull out the faulted cable and pull in new and terminate it rather than search dig and splice.

Those drive in Mailbox spikes that go on the end of a 4x4 post are long enough to reach almost anything in the ground. Call before you dig or drive anything in the ground.


 o
RE: POCO cable upgrades in neighborhood

Underground is preferred by those who do not like their visual faculties offended. And buried does offer some storm protection- for the buried portion. With lines on poles, changes in the system can often be done with no interruption of service. Temporary jumpers are installed providing two paths for the voltage while the new conductor is installed to replace the old. Not easy to do with the buried installation.


 o
RE: POCO cable upgrades in neighborhood

30 inches requires a very large 'ditch witch' type unit.

The common ones I see barely go 18 inches.

"Temporary jumpers are installed providing two paths for the voltage while the new conductor is installed to replace the old. "

Temporary jumpers are used to carry the whole load if required.

the new overhead lines are installed and connected on the load side.
the feed end is then connected, and the old disconnected and removed.

120 V 'bare hand' work is not nearly as dangerous as 7.2 kV (and higher) feeder 'bare hand' work.


 o
RE: POCO cable upgrades in neighborhood

Just for the sake of conversation, they are using directional drilling to bore what I think would be conduit first and then the new wire pulled thru?

They appear ready to begin the project as the large drills and spools of wire/conduit have arrived in the neighborhood.

About 10 years ago they used similar drills to pull new telephone fiber optic cable... I assume these high voltage lines will be a much bigger undertaking.


 o
RE: POCO cable upgrades in neighborhood

High voltage lines just need larger conduit.

Some places forced all new POCO wiring to be underground many years ago.
No more poles and overhead lines allowed.

It does crate some comedy when a new house in an old neighborhood is the only one with an underground feed.

The poles are still there, carrying both distribution line (high voltage) and service lines to all the other houses, but one house will have an underground feed.
It is run down the side of the nearest pole and then to the house.


 o
RE: POCO cable upgrades in neighborhood

Grandmum, might I suggest that when there are crews
at the work site, you politely ask them about any outages that you may experience during the project And, just out of
curiosity, ask them why you weren't notified, if it
is going to be of a lengthy duration.


 o
RE: POCO cable upgrades in neighborhood

"why you weren't notified"

Usually there is no requirement to notify users of disruptions for maintenance.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.